5-186
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.11 IEC 61850 CONFIGURATION
CHAPTER 5: SETPOINTS
Figure 5-61: LD name configuration
MMXU parameters:
The MMXU deadband settings represent the deadband values used to determine when updating the MMXU.mag. and
.cVal. values from the associated .instmag. and .instcVal. values.
The .mag. and .cVal. values are used for the IEC 61850 buffered and unbuffered reports. These settings correspond to the
associated .db data items in the CF functional constraint of the MMXU logical node, as per the IEC 61850 standard.
According to IEC 61850-7-3, the db values represent the percentage of difference between the maximum and the
minimum in units of 0.00%. Thus, it is important to know the maximum value for each MMXU measured quantity, since this
represents the 100.00% value for the deadband. The minimum value for all quantities is 0; the maximum values are as
follows:
A value of 1000 represent the 1% of the scale.
The minimum and maximum main values (secondary) are:
-For Current 0 to 160 A
-For Voltage 0 to 300 V
-For frequency 20 to 70 Hz
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...