CHAPTER 5: SETPOINTS
5.5 CONTROL ELEMENTS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-111
The Closing process using anticipative algorithm is described on the following figure:
Figure 5-25: Anticipative algorithm
Where:
V
ref
Referenced phasor (the one with lower frequency)
V
s
Actual voltage phasor (the one with lower frequency)
V’
s
Calculated voltage phasor, depending on the set breaker closing time (anticipative algorithm)
j
360º *TCB *Df = Calculated angle for phasor V’
s
TCB
Breaker Closing time defined by setting
Df
Frequency slip (mHz) between phasors
j
1
Angle difference set as maximum angle difference (
Dj
set ,
Max Angle Difference)
j
2
=
Angle difference between V
ref
and V
s.
The algorithm starts operating when
j
2
equals two times the angle
set as maximum angle difference.
Closing permission is given when
V’
s
is over
V
ref
, which means that line and busbar voltages are in phase.
If the frequency slip is high, it is possible that as soon as the window defined by two times the maximum angle difference
(
j
2
) is entered, the relay produces a closing permission output, if it is guaranteed that the projected phasor is within the limit
marked by the setting, as shown in the following figure. Besides, when the product of frequency slip and breaker close
time goes beyond this window, closing is not allowed.
Figure 5-26: High slip closing permission signal
V
Ref
V
1
2
V’
s
V
Ref
V
1
2
V’
s
1
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...