CHAPTER 11: APPLICATION EXAMPLES
11.2 EXAMPLE 2: TOC PROTECTION & RECLOSING SETTINGS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
11-5
11.2 Example 2: TOC protection & reclosing settings
11.2.1 Description
The purpose of this exercise is to introduce the F650 User about the way to set a protection scheme including:
Trip operation of a phase time overcurrent protection.
Two reclosing shots with successful fault clearing.
Synchronism check action to verify two ends voltage conditions previous to perform each reclosing action.
11.2.2 Communicate with the relay
This procedure is described in Example Nº 1. Therefore check the actual PC communication status to assure a fast and
reliable communication with F650 relay.
11.2.3 Set the protection function
This procedure is fully described in paragraph 13.3 (see Example Nº 1). Therefore it is not necessary to explain it here again
except about the small modifications required for the actual exercise, as well the additional settings not used until now (i.e.
recloser and synchrocheck).
Therefore, by having the F650 set like in the previous exercise (paragraph 13), the new settings and changes to be done in
the relay to work in a protection-reclosing scheme are:
Under
SETPOINT
SYSTEM SETUP
BREAKER
BREAKER SETTINGS
Under
SETPOINT
INPUTS/OUTPUTS
CONTACT I/O
BOARD F
Under
SETPOINT
RELAY CONFIGURATION
PROTECTION ELEMENTS
Name
Value
Number of Switchgear
1
Name
Value
Output Logic_00_00
Positive
Voltage Threshold B_00
80V
Debounce Time B_00
10 ms
Input Type_00_00 (CC1)
Positive
Delay Input Time_00_00 (CC1)
0 ms
Output Type_00_00
Normal
Pulse Output Time_00_00
500 ms
Select
Source
OR
AR Initiate
Press for Logic
Phase TOC A Op
Phase TOC B Op
Phase TOC C Op
AR Conds Input
Synch Close Perm
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...