11-8
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
11.3 EXAMPLE 3: SET AN OPERATION
CHAPTER 11: APPLICATION EXAMPLES
11.3 Example 3: Set an operation
11.3.1 Description
This simple operation describes how to program and set an operation command on the F650 relay. In the present case
the operation is:
To configure some F650 output contact to be operated since the front of the relay.
To set some LED to show the operation of the output contact (while being closed).
To close a F650 output contact using a front key pushbutton.
To reset the output contact and LED using another front key pushbutton.
11.3.2 Procedure
Set the following values:
Under
SETPOINT
CONTROL ELEMENTS Þ INPUTS/OUTPUTS
BOARD F
*
This setting is non-relevant since it applies only when “
pulse
” type is chosen
Under
SETPOINT
RELAY CONFIGURATION
OUTPUTS
Under
SETPOINT
RELAY CONFIGURATION
LEDS
Name
Value
Output Logic_00_00
Positive
Output Type_00_00
Latch
Pulse Output Time
10000ms
*
Select
Name
Source
Contact Output Operate 00 (Board F)
C_Output Oper_00_00
Operation_bit000
Contact Output Reset 00 (Board F)
C_Output Reset_00_00
Operation_bit001
Select
Name
Source
Led 14
Close Contact_00_00
C_Output_00_00
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...