5.5 CONTROL ELEMENTS
CHAPTER 5: SETPOINTS
Care must be taken when configuring the delay for an IOC or TOC element that is being supervised by CT Supervision
Failure function. The delay time in the IOC function should be set to a value 10 ms greater than CT Supervision Failure
delay timer
5.5.12 Second harmonic inhibit
For firmware 7.50 or above, the F650 incorporates one Second Harmonic Inhibit element which can be used to block
sensitive elements when particular level of inrush currents is detected in phase currents.
During transformer energization, the inrush current presenting in phase currents may impact some sensitive elements,
such as neutral directional overcurrent. Therefore, the ratio of the second harmonic to the fundamental magnitude per
phase is monitored, while exceeding the settable pickup level, an inhibit signal is asserted, which can be used to block such
sensitive elements. In order to get proper functionality, 2
nd
Harmonic Inhibit delay must be minor than delay of IOC or TOC
element that is being supervised by 2
nd
Harmonic inhibit function.
Second harmonic function settings are available in Enervista 650 setup at
Setpoint > Control Elements > 2
nd
HRMC
Inhibit
Function
This setting allows enabling and disabling the 2
nd
Harmonic Inhibit function.
2nd HRMC PICKUP
This setting sets the Phase Current 2nd Harmonic value required to allow the Second
Harmonic Inhibit element to pick up.
2nd HRMC DELAY
This setting specifies the pickup time delay for this function to operate after pickup.
Note that
MINIMUM CURRENT
Sets the minimum value of fundamental secondary current required to allow the
Second Harmonic Inhibit element to operate.
If Phase for Operation is set to AVERAGE, the average of three-phase currents is used
for supervision. The similar adaptive average algorithm is applied to calculate the
average of operation current magnitude.
PHASES FOR OPERATION
This setting defines the phases required for operation, and the detail is explained
below:
•
ANY ONE: At least one phase picked up.
•
ANY TWO: Two or more phases picked up.
•
ALL THREE: All three phases picked up.
•
AVERAGE: The average of three-phase harmonics picked up.
If set to AVERAGE, the relay calculates the average level of the second harmonic and
compares this level against the pickup setting. Averaging of the selected harmonic
follows an adaptive algorithm depending on the fundamental current magnitude per-
phase. Only phases where the fundamental current exceeds the cut-off level are
included in the average.
SETPOINTS ð CONTROL ELEMENTS ð 2
nd
HRMC Inhibit
SETTING DESCRIPTION NAME
DEFAULT VALUE
STEP
RANGE
Function
Function
DISABLED
N/A
[DISABLED – ENABLED]
Second harmonic
pickup
2ND HRMC PICKUP
1
1%
[1- 40.00]
Second harmonic delay 2ND HRMC DELAY
0.00
0.1s
[0.00-600.00]
Minimun secondary
current to operate
MINIMUM. CURRENT
0.05
0.01A
[0.05-15.00]
Phase affected to
operate
PHASES FOR
OPERATION
ANY ONE
N/A
[ANY ONE- ANY TWO- ALL THREE- AVERAGE]
Snapshot events
Snapshot events
DISABLED
N/A
[DISABLED – ENABLED]
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...