4-30
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
4.1 ENERVISTA 650 SETUP SOFTWARE
CHAPTER 4: INTERFACES, SETTINGS & ACTUAL VALUES
Table 4-11: Control elements, actual values menu, firmware version 7.50 and above
Table 4-12: Records status, actual values menu
4.1.8.3 Metering
The Metering menu includes all the measurements available in the device. Primary and secondary values, and also the
data related to the recording functions in the relay
Control Elements
Frequency
Status signals (pickups and operations) for under, overfrequency and frequency rate of
change units.
Synchrocheck
Status signals for synchrocheck function (25).
Autoreclose
Status signals for autoreclose function (79). Close signal, recloser status (ready, lockout, etc.),
block signals after each shot.
Breaker Failure
Status signals for breaker failure function (50BF).
VT Fuse Failure
Fuse failure detection signal.
Broken Conductor
Status signals (pickups and operations) for broken conductor (I2/I1).
Setting Groups
Status signals (activations and blocks) for the relay setting group change. By default the
Setting Groups
setting is disabled and all the grouped elements can be enabled at the same
time.
Locked Rotor
Status signals (pickups and operations) for locked rotor units.
Pulse Counters
Status signals for pulse counters units.
Analog Comparator
Status signals for analog comparator units.
Load Encroachment
Status signals (pickups and operations) for load encroachment units.
Max. Number of Starts
Status signal for number of starts operations
Digital Counters
Status signals for the Digital Counter units.
Cold Load Pickup
Status signals for the Cold Load Pickup Function.
60CTS Failure
Status signals of Current transformer failure Function
2nd HRMC Inhibit
Status signals of Second Harmonic Inhibit Function
Record Status
Fault Reports
This menu shows the fault report status signals, as fault report trigger, fault date, fault type
and location, besides the fault report number.
Control Events
Status of the control events (if the signal configured to launch the control event is active or
not).
Oscillography
Status of signals related to oscillography recording, such as status or digital channels,
oscillography trigger, number of records available, etc.
Data Logger
Data logger information about oldest and newest sample time stamp, and number of
channels and days configured in data logger settings.
Demand
Demand trigger and reset inputs status.
Energy
Freeze, unfreeze and reset input signals for energy counters.
Breaker Maintenance
All signals related to breaker maintenance, such as number of openings, closings, (KI)
2
t
counters, alarm signal for (KI)
2
t, etc.
metering
Primary Values
Primary values measurements for currents, voltages, power, energy and demand
Secondary Values
Secondary values measurements for currents, voltages and power.
Phasor Diagram
Current, voltage and sequence components.
Frequency
Line and Bus frequencies.
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...