CHAPTER 9: BOOTCODE AND FIRMWARE UPGRADE
9.1 FIRMWARE UPGRADE VERSIONS BELOW 7.00.
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
9-3
9.1.1 Communication parameters
1.
Ethernet Connection/Type - Both boot code and firmware upgrade processes require Ethernet communications. It is
strongly recommended to use a direct connection between the PC and the relay using a Cross-Over RJ45 Ethernet
cable, instead a direct connection through a hub or switch. Upgrading through Local Area Network (LAN) must be
avoided.
Serial RS232 Communication - Serial communication is necessary only to perform the bootware upgrade for versions
previous to 7.00.
2.
Relay IP Address - An IP address must be assigned to the relay in the Ethernet parameters via HMI at
Product Setup >
Communication > Ethernet > Ethernet1
menu, or via Enervista 650 Setup software at
Setpoint > Product Setup >
Communication Settings > Network (Ethernet) 1
as shown in the table below:
Table 9-1: Ethernet parameters
3.
PC IP Address - In case the boot code has been previously updated to the relay (section 9.2), the IP address and other
parameters already assigned in the process are:
IP Address:192.168.37.177
Netmask:255.255.255.0
Gateway:192.168.37.10
Then the PC settings should be the same pattern as follows:
IP Address:192.168.37.xxx
Netmask:255.255.255.0
Gateway:192.168.37.10 (if desired)
Where XXX is a number between 0 and 255 that is not assigned to any other device to avoid collisions.
4.
Other Network, Communications and Data Flow checks
•
According to the model number of the relay, to enable the 10/100 BASE TX-CABLE option in the relay communication
board, a specific jumper in this board must be changed. See detailed instructions in paragraph 3.4.3 of Instruction
Manual GEK-106310AE.
•
IP address, netmask, gateway are correct and match the parameters used in the computer to perform the procedure.
See table 9.1 (on this chapter) of Manual GEK-106310AE
COMMUNICATION PARAMETERS.
Product Setup > Communication Settings > Network (Ethernet) 1
Name
Value
Units
Range
IP Address Oct1
192
[0 : 255]
IP Address Oct2
168
[0 : 255]
IP Address Oct3
37
[0 : 255]
IP Address Oct4
177
[0 : 255]
Netmask Oct1
255
[0 : 255]
Netmask Oct2
255
[0 : 255]
Netmask Oct3
255
[0 : 255]
Netmask Oct4
0
[0 : 255]
Gateway IP Oct1
192
[0 : 255]
Gateway IP Oct2
168
[0 : 255]
Gateway IP Oct3
37
[0 : 255]
Gateway IP Oct4
10
[0 : 255]
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...