5-46
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.4 PROTECTION ELEMENTS
CHAPTER 5: SETPOINTS
Table 5-20: Setting group settings
Setting Group settings are as follows:
Function:
Possible values are: [DISABLED – ENABLED]
When this setting is DISABLED, the relay is working in single setting group mode. All protection elements that belong to the
group selected in the active groups setting are available and working at the same time if required.
If this setting is ENABLED, the relay is working in multiple setting groups mode. In this mode, all protection elements of
different setting groups are available to be activated. However, only protection elements of the Active Group selected are
real active ones. In this case, selection of active setting group can be modified through logic signals.
I
Active group:
Possible values are 1, 2, 3, 4, 5 or 6.
This setting indicates which setting group is active by default. Default configuration value is 1.
•
When this function is disabled, the Active Group value indicates which setting group of protection elements is
available, e.g if Active Group is GROUP 1, all protection elements under setting group 1 in
SetPoint > Protection
Elements
are available.
•
When this function is enabled, the Active Group value indicates the active setting group when no group is selected as
the active one.
Snapshot events:
Possible values are: [DISABLED – ENABLED]
If this setting is ENABLED, Snapshot events related to change of setting groups are reported.
Regarding changing between setting groups when working in multiple setting groups mode, the Relay incorporates
several signals associated with the Protection elements grouping in tables.
First, signals that indicate the group activation:
GROUP 1 ACT ON: This signal produces the activation of setting group 1
GROUP 2 ACT ON: This signal produces the activation of setting group 2
GROUP 3 ACT ON: This signal produces the activation of setting group 3
GROUP 4 ACT ON: This signal produces the activation of setting group 1
GROUP 5 ACT ON: This signal produces the activation of setting group 2
GROUP 6 ACT ON: This signal produces the activation of setting group 3
Priority of activation signals is indicated as follow:
GROUP 6 > GROUP 5 > GROUP 4 > GROUP 3 > GROUP 2 > GROUP 1
E.g: If group 4 and group 1 are selected at the same time, setting group 4 is the active one due to the higher priority level.
As previously mentioned, when no activation signal is selected, the default group set in Enervista 650 Setup under
Setpoint > Control Elements > Setting Group > Active group
is the active group.
These activation signals for the different setting groups can be configured using EnerVista 650 Setup at
Setpoint > Relay
Configuration > Control Elements
as shown. Different inputs can be linked to different activation signals.
Setpoint > Control Elements > Setting Group
Setting Description
Name
Default Value Step
Range
Setting Grouping Permission
Function
DISABLED
N/A
[DISABLED – ENABLED]
Active Group
Active Group
GROUP 1
N/A
[GROUP 1 – GROUP 2 – GROUP 3- GROUP 4-
GROUP 5-GROUP 6]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...