6-12
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
6.2 STATUS
CHAPTER 6: ACTUAL VALUES
The AUTORECLOSE INTERNAL STATUS are internal signals provided by the autoreclose unit:
AR CLOSE BREAKER:
Breaker close command given by the autoreclose
AR OUT OF SERVICE:
Autoreclose out of service (Disabled)
AR READY:
Autoreclose in service
AR LOCKOUT:
Autoreclose in lockout status (finished cycled-definite trip)
AR BLOCK:
Autoreclose blocked (by input, logic, others, etc).
AR RCL IN PROGRESS:
Cycle in course (autoreclose in progress).
AR LCK BY ANOMALY:
Autoreclose in “Lockout” by anomaly.
AR LCK BY FAIL OPEN:
Autoreclose in “Lockout” by a failure in opening the breaker.
AR LCK BY FAIL CLOSE:
Autoreclose in “Lockout” by a failure in closing the breaker.
AR LCK BY USER:
Autoreclose in “Lockout” by manual close.
AR LCK BY CONDS:
Autoreclose in “Lockout” by conditions. See input conditions configuration.
AR LCK BY TRIPS:
Autoreclose in “Lockout” by maximum number of trips.
AR LCK BY SHOTS:
Autoreclose in “Lockout” at the end of cycle – Definite trip.
AR BLK AFTER 1 SHOT:
Signal sent by the autoreclose after the 1
st
shot.
AR BLK AFTER 2 SHOT:
Signal sent by the autoreclose after the 2
nd
shot.
AR BLK AFTER 3 SHOT:
Signal sent by the autoreclose after the 3
rd
shot.
AR BLK AFTER 4 SHOT:
Signal sent by the autoreclose after the 4
th
shot.
AR BLOCK BY LEVEL:
Autoreclose blocked by level. See AR block signals configuration
AR BLOCK BY PULSE:
Autoreclose blocked by pulse. See AR block signals configuration
AR STATUS:
Autoreclose status (in service – out of service)
AR LOCKOUT MODE:
Relay “Lockout” status.
AR BLOCK MODE:
Relay “Block” status
AutoRecSt_61850: Autorecloser status sent in IEC 61850. This value represent whether or not the auto reclosing is ready, in
progress or successful. It is an enumerate type whose values are defined in IEC 61850-7-4 Edition 2.0 standard and it is
available
6.2.4.4 Breaker failure
This screen can be accessed at
Actual> Status > Control Elements >
Breaker Failure
, and it includes the following
signaling LEDs for the breaker failure function:
Table 6-13: Breaker failure actual values
BKR FAIL INITIATE
External signal for breaker failure initiation. (configurable at
Settings> Relay Configuration >
Protection Elements
).
BKR FAIL NO CURRENT
Signal for breaker failure without current
BREAKER FAILURE ACTUAL VALUES
BKR FAIL INITIATE
BKR FAIL NO CURRENT
BKR FAIL SUPERVISION
BKR FAIL HISET
BKR FAIL LOWSET
INTERNAL ARC
BKR FAIL 2nd STEP
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...