CHAPTER 5: SETPOINTS
5.2 PRODUCT SETUP
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-17
5.2.3 Fault report settings
The fault report module defines the type of fault (three-phase, phase-to-phase, phase-to-ground), and the distance to the
fault. The fault activation signal (FAULT REPORT TRIGG) is programmed at
Setpoint > Relay Configuration > Protection
Elements
.
The fault report provides fault date, fault type and fault location information.
Information referred to the last ten faults is stored as fault report and available to the user through the EnerVista 650 Setup
software or the web server application. Each fault report includes the following information:
•
Fault date and time
•
Pre-fault current and voltage in primary values
•
Fault current and voltages in primary values
•
Fault type
•
Distance to the fault (fault location)
•
Line parameters
•
Recloser and breaker status information
As an option, the Relay offers the possibility to display a fault-warning message on the relay HMI (selectable by setting).
5.2.3.1 Fault report settings
Function permission (Function):
Enabling this setting allows to create a fault report
when the FAULT REPORT TRIGG is activated.
Positive sequence impedance module (Pos Seq Module):
Value, in ohms, of the line positive sequence
impedance module.
Positive sequence impedance Angle (Pos Seq Angle):
Value, in degrees, of the line positive sequence angle.
Zero sequence impedance module (Zero Seq Module):
Value, in ohms, of the line zero sequence impedance
module.
Zero sequence impedance Angle (Zero Seq Angle):
Value, in degrees, of the line zero sequence angle.
Line Length:
The metering element can be kilometers or miles.
Show Fault On HMI:
This setting enables or disables the option to display
faults on the Relay HMI.
Snapshot Events:
This setting enables or disables the snapshot event
generation for the fault report element.
CT Direction:
Direction of the phase current transformers.
Forward: The polarity of he current transformers is as
the F650 wiring diagram.
Setpoint > Product Setup > Fault Report
Setting Description
Name
Default Value
Step
Range
Function permission
Function
DISABLED
N/A
[DISABLED – ENABLED]
Positive sequence impedance module
Pos Seq Module
3.00
0.01 Ohm
[0.01 : 250.00]
Positive sequence impedance angle
Pos Seq Angle
75
1 Deg
[25 : 90]
Zero sequence impedance module
Zero Seq Module
9.00
0.01 Ohm
[0.01 : 750.00]
Zero sequence impedance angle
Zero Seq Angle
75
1 Deg
[25 : 90]
Line length
Line Length
100.0
0.1
[0.0 : 2000.0]
Display fault on HMI
Show Fault On HMI
DISABLED
N/A
[DISABLED – ENABLED]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
CT Direction
CT Direction
REVERSE
N/A
REVERSE-FORWARD
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...