1-18
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
1.3 ENERVISTA 650 SETUP SOFTWARE
CHAPTER 1: GETTING STARTED
1.3.3 Connecting EnerVista 650 Setup to the F650
This section is intended as a quick start guide to using the EnerVista 650 Setup software. Refer to section 4.1 in this manual
for more information about the EnerVista 650 Setup software interface.
1.3.3.1 Configuring an Ethernet connection
Before starting, verify that the Ethernet network cable is properly connected to the Ethernet port on the back of the relay.
1.
Install and start the latest version of the EnerVista 650 Setup software (available from the GE EnerVista DVD or online
from
http://www.gegridsolutions.com/multilin
(see previous section for installation instructions).
2.
Go to
Communication > Computer
.
3.
Select
Control Type
as
MODBUS TCP/IP
from the drop-down list. This option displays a number of interface
parameters that must be entered for proper Ethernet communications.
4.
Enter the relay IP address (from
Setpoint > Product Setup > Communication Settings > Network > IP Address
) in the
IP Address
field in
MODBUS TCP/IP SETUP
.
5.
Enter the relay ModBus address (from
Setpoint > Product Setup > Communication Settings > ModBus Protocol >
ModBus Address COM1/COM2 setting
) in the Unit Identifier (Slave Address) field.
6.
Enter the ModBus port address (from
Setpoint > Product Setup > Communication Settings > ModBus Protocol >
ModBus Port Number
setting) in the ModBus Port field.
7.
The Device has now been configured for Ethernet communications. Click
ON
to begin communicating.
1.3.3.2 Configuring the RS232 connection
Before starting, verify that the RS232 serial cable, or the USB Cable, is properly connected to the RS232port or the USB port
on the front panel of the relay.
1.
http://www.gegridsolutions.com/index.htm
(see previous section for installation instructions).
2.
Go to
Communication > Computer
and enter the following data referred to communications:
3.
Under
Control Type
select
No Control Type
from the drop-down list.
4.
Enter the relay Slave Address (
Setpoint > Product Setup > Communication Settings > ModBus Protocol
) in the Slave
Address field. The default value is 254.
5.
Enter the physical communications parameters (Baud rate and parity settings) from the
Setpoint > Product Setup >
Communication Settings > Serial Ports
menu. Default values are 19200 for baud rate and none for parity.
6.
The unit has now been configured for RS232 communications. Click
ON
to begin communicating.
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...