6-10
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
6.2 STATUS
CHAPTER 6: ACTUAL VALUES
6.2.4.2 Synchrocheck
This screen can be accessed at
Actual> Status > Control Elements >
Synchrocheck
, and it includes the following signaling
LEDs for the synchronism check function:
Table 6-11: Synchrocheck actual values
Synchrocheck BLK INP:
Block signal for the synchrocheck unit, configurable at
Setpoint > Relay
Configuration > Protection Elements
Synchrocheck OP:
Closing permission signal in live line-live bus conditions with open breaker.
SYNCHK CLOSE PERM:
General Closing permission of the Synchronism unit. It contemplates all possible
situations, live line-live bus conditions, and the closing permission logics (dead line-
dead bus, live line- dead bus, dead line-live bus).
Note
: in case the Function is disabled,
the Closing permission signal is activated in order not to interfere with possible logics
where it is included. If the synchronism unit is enabled, this signal only activates under
the closing conditions established by setting.
Synchrocheck COND OP:
Closing permission according to permission logics (DL-DB, LL-DB, DL-LB).
DL-DB OPERATION: Closing permission in dead line – dead bus condition.
DL-LB OPERATION: Closing permission in dead line – live bus condition.
LL-DB OPERATION: Closing permission in live line – dead bus condition.
SLIP CONDITION:
Internal signal indicating frequency slip between the line voltage and bus voltage
phasors.
BUS FREQ > LINE FREQ:
Busbar Frequency higher than line frequency
BUS FREQ < LINE FREQ:
Busbar Frequency lower than line frequency
VOLTAGE DIFFERENCE
:
Voltage difference between the line and the busbar in volts (secondary values), only
available if the Synchrocheck element is enabled.
FREQ. DIFFERENCE
:
Frequency difference between the line and the busbar in Hz, only available if the
Synchrocheck element is enabled.
6.2.4.3 Autoreclose
This screen can be accessed at
Actual> Status > Control Elements >
Autoreclose
, and it includes the following signaling
LEDs for the Autoreclose function:
Table 6-12: Autoreclose actual values
SYNCHROCHECK ACTUAL VALUES
Synchrocheck BLK INP
Synchrocheck OP
SYNCHK CLOSE PERM
Synchrocheck COND OP
DL-DB OPERATION
DL-LB OPERATION
LL-DB OPERATION
SLIP CONDITION
BUS FREQ > LINE FREQ
BUS FREQ < LINE FREQ
VOLTAGE DIFFERENCE
FREQUENCY DIFFERENCE
AUTORECLOSE INPUTS
AR LEVEL BLOCK
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...