5-158
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.9 RELAY CONFIGURATION
CHAPTER 5: SETPOINTS
5.9.3 Operations
This menu option shows the settings for the 24 control operations that can be programmed, as follows:
•
Select
checkbox enables the desired operation.
•
Command Text
setting defines the command name.
•
Interlocks Type
setting defines the desired interlock type (An interlock is a condition that must be fulfilled for an
operation to be performed). The possible options are
Logic
or
None.
If the
LOGIC
option is selected, the program
enables a new window for creating the logic. If the
NONE
option is selected, then the following setting (
Interlocks
) is
irrelevant.
•
Interlocks
setting define the desired interlocks. This setting is enabled selecting the “
logic
” option in “
Interlock type
”.
In the “
Interlock logic
” screen we can set the interlock logic, as shown on Figure 5-48: Operations and interlocks
The settings on this screen allow creating a logic configuration with up to 3 AND gates and 1 OR gate for each of the
24 operations available in the relay. These settings are:
Select
–
Enables/disables the selection for the interlock input
Source
–
Selects a function, digital input, logic, etc. for defining each input of each AND gate.
NOT
–
Logic inverter
Figure 5-48: Operations and interlocks
•
Final State
Type
setting: defines whether the operation requires (in addition to the interlock logic) any other conditions
to determine a “success condition”. If so, we must select LOGIC. Otherwise, we must select NONE.
•
Final State
setting: defines the success condition of a programmed operation, if the previous setting (
Final State type
)
was set as LOGIC.
•
Front Key
setting: defines the front pushbutton from which the operation can be executed.
•
Contact Input
setting: defines whether the operation can be executed by digital input. It defines the digital input to be
used for this purpose.
•
Virtual Output
setting: defines whether the operation can be executed from a virtual output previously defined at the
logic configuration tool (PLC logic).
•
Time Out
setting: defines the period during which the operation command remains activated waiting for a success
condition. If the success signal is received before this period expires, the command signal is removed and the timer
reset. If the success condition is not received within this period of time, the operation is considered to be finished.
•
HMI setting:
defines whether the operation can be executed by HMI
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...