CHAPTER 10: COMMISSIONING
10.17 RECLOSER (79)
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
10-23
10.17.2 Recloser status
BLOCK
Activate the block input and verify that the recloser is in BLOCK status.
Close the breaker and wait for 5 seconds.
Command a trip and verify that the breaker opens but there is no reclose.
INHIBITION BY RECLOSING CONDITIONS
Close the breaker and wait for 5 seconds.
Command a trip, verify that the breaker opens and wait for the first shot.
Activate the inhibition input and command a new trip.
Verify that the breaker opens, wait for 8 seconds and verify that the relay does not reclose.
10.17.3 External reclose initiation
Close the breaker and wait for 5 seconds.
Activate the reclose initiation input and open the breaker, verify that the relay executes the first shot
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...