10-24
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
10.18 THERMAL IMAGE ELEMENT (49)
CHAPTER 10: COMMISSIONING
10.18 Thermal image element (49)
Disable all protection elements except for Thermal Model (49).
Set the pickup level to 2 A.
Set the time constant t1 to 3 minutes and t2 to one time t1.
Apply currents of 2, 5, and 10 times the tap and ensure that the operation times are within the range described on the
following table:
After each measuring, the thermal element must be reset to zero in order to start the next test at a zero thermal status
condition.
Repeat the test selecting a time constant t1 of 60 minutes. Verify that the operation time is within the range described on
the following table:
After each measuring, the thermal element must be reset to zero in order to start the next test at a zero thermal status
condition.
Rated Current (A)
Applied Current (A)
Times de set tap
Operation time (s)
4.0
2
48.5 - 53.6
5
10.0
5
7.06 - 7.80
20.0
10
1.77 - 1.95
Rated Current (A)
Applied Current (A)
Times de set tap
Operation time (s)
4.0
2
960 - 1072
5
10.0
5
141 - 156
20.0
10
35.4 - 39
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...