5-136
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.6 INPUTS/OUTPUTS
CHAPTER 5: SETPOINTS
5.6.2 Control settings for input/output
Configuration of settings relative to inputs and outputs can only be accessed through the EnerVista 650 Setup
software, and not via the HMI
. For this purpose, the user must access
Setpoint > Inputs/Outputs > Contact I/O > Board
X
, being X the corresponding I/O board.
settings relative to I/O boards are described in Table 5-83: I/O board settings
Table 5-83: I/O board settings
For versions previous to 7.00, the snapshot event setting enables or disables the snapshot event generation for this
element. It is mandatory to enable this setting in order the input/output values to be refreshed in IEC61850 protocol
.
Being:
X
F, G, H or J, the I/O board name, depending on the Relay model.
F and G are internal Relay boards, and H and J are additional boards available in CIO modules (remote Bus CAN I/O
module).
SETPOINT > INPUTS/OUTPUTS > CONTACT I/O >
BOARD F > BOARD G > BOARD H > BOARD J
SETTING DESCRIPTION
NAME
DEFAULT VALUE STEP
RANGE
I/O board type (available only for CIO modules)
I/O Board Type_
X
NONE
N/A
[NONE,
16 INP + 8OUT,
8 INP + 8OUT + SUPV,
32 INP
16 INP + 8 ANA]
Input activation voltage threshold Group A
Voltage Threshold A_
X
80
1 V
[10 : 230]
Input activation voltage threshold Group B
Voltage Threshold B
_X
80
1 V
[10 : 230]
Input activation voltage threshold Group C
Voltage Threshold C_
X
80
1 V
[10 : 230]
Input activation voltage threshold Group D
Voltage Threshold D
_X
80
1 V
[10 : 230]
Debounce time for Group A
Debounce Time A
_X
15
1 ms
[1 : 50]
Debounce time for Group B
Debounce Time B
_X
15
1 ms
[1 : 50]
Debounce time for Group C
Debounce Time C
_X
15
1 ms
[1 : 50]
Debounce time for Group D
Debounce Time D
_X
15
1 ms
[1 : 50]
Input type
Input Type_
X
_CC
Y
(CC
Y
)
POSITIVE
N/A
[POSITIVE-EDGE,
NEGATIVE-EDGE,
POSITIVE,
NEGATIVE]
Input signal time delay
Delay Input Time_
X
_CC
Y
(CC
Y
)
0
1 ms
[0 : 60000]
Output logic type
Output Logic_
X
_0
Z
POSITIVE
N/A
[POSITIVE,
NEGATIVE]
Output type
Output Type_
X
_0
Z
NORMAL
N/A
[NORMAL,
PULSE,
LATCH]
Output pulse length
Pulse Output Time_
X
_0
Z
10000
1 ms
[0 : 60000]
Analog Inputs Range
Range_
X
_0
Z
NONE
N/A
[NONE,
-1 to 0mA,
0 to 1 mA,
-1 to 1 mA,
0 to 5 mA,
0 to 10 mA]
Minimum Value
Min_Value_
X
_0
Z
0.00
0.01
[ -9999.99 : 9999.99]
Maximum Value
Max_Value_
X
_0
Z
0.00
0.01
[ -9999.99 : 9999.99]
Snapshot event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...