F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
D.4 IEC 104 SETTINGS
APPENDIX D: IEC 60870-5-104 PROTOCOL
Function:
Enable or disable the protocol operation for the first IEC 60870-5-104
connection.
TCP Port:
Listening TCP port in the relay. Default value is 2404.
Common Addr of ASDU:
Address in the ASDU header. Default value is 255.
Cyclic Meter Period:
Number of seconds for cyclical data sending, 0 means no spontaneous
meterings.
Synchronization event:
Period of time (in minutes) for which timestamps are considered valid after
receiving a clock synchronization command.
IEC104 NET1 CLI1 OCTET1 to 4:
These four octets define the IP address of the first client that is accepted in
the first connection. The F650 relay can respond to a maximum of 2 IEC
60870-5-104 masters (not at the same time) in this connection.
EC104 NET1 CLI2 OCTET1 to 4:
These four octets define the IP address of the second client that is accepted
in the first connection. The F650 relay can respond to a maximum of 2 IEC
60870-5-104 masters (not at the same time) in this connection.
Function 2:
Enable or disable the protocol operation for the second connection.
TCP Port 2:
Listening TCP port in the relay. Default value is 2404.
Common Addr of ASDU2:
Address in the ASDU header. Default value is 255.
IEC104 NET2 CLI1 OCTET1 to 4:
These four octets define the IP address of the first client that is accepted in
the second connection. The F650 relay can respond to a maximum of 2 IEC
60870-5-104 masters (not at the same time) in this connection.
IEC104 NET2 CLI2 OCTET1 to 4:
These four octets define the IP address of the second client that is accepted
in the second connection. The F650 relay can respond to a maximum of 2
IEC 60870-5-104 masters (not at the same time) in this connection.
I
EC104 SCALE CURRENT, VOLTAGE,
POWER, ENERGY, OTHER:
These settings are numbers used to scale Analog Input point values. These
settings group the F650 Analog Input data into types: current, voltage,
power, energy, and other. Each setting represents the scale factor for all
Analog Input points of that type. For example, if the
IEC104 SCALE VOLTAGE
is set to a value of 1000, all IEC104 Analog Input points that are voltages are
returned with the values 1000 times smaller (e.g. a value 72000 V on the
F650 is returned as 72). These settings are useful when Analog Input values
must be adjusted to fit within certain ranges in IEC 60870-5-104 masters.
Note that a scale factor of 0.1 is equivalent to a multiplier of 10 (i.e. the value
is 10 times larger).
IEC104 DEADBAND CURRENT,
VOLTAGE, POWER, ENERGY, OTHER:
These settings are the values used by the F650 to determine when to trigger
spontaneous responses containing Analog Input data.
These settings group the F650 Analog Input data into types: current,
voltage, power, energy, and other. Each setting represents the default
deadband value for all Analog Input points of that type. For example, in
order to trigger spontaneous responses from the F650 when any current
values change by 15 A, the
IEC104 DEADBAND CURRENT
setting should be
set to 15. Note that these settings are the default values of the deadbands.
Parameter of measured value ASDU can be used to change deadband
values, from the default, for each individual IEC104 Analog Input point.
Whenever power is removed and re-applied to the F650, the default
deadbands are in effect.
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...