5-104
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.5 CONTROL ELEMENTS
CHAPTER 5: SETPOINTS
5.5.2 Synchronism check element - synchrocheck (25)
Note:
The Switchgear element used in the F650 synchronism element is the one configured in the
Number of Switchgear
setting inside
Breaker settings
, at “
Setpoint > System Setup > Breaker > Breaker Settings
”.
The synchronism element is used for monitoring the connection of two parts of the circuit by the close of a breaker. This
element verifies that voltages (V1 and V2) at both sides of the breaker are within the magnitude, angle and frequency limits
set by the user. V1 and V2 are the line and busbar voltage values measured by the relay.
Synchronism check (25) is defined as the comparison of the voltage difference of two circuits with different sources to be
either linked through an impedance element (transmission line, feeder, etc.), or connected through parallel circuits of
defined impedance (Figure 5-23: Synchromism check element) The voltage comparison between both sides of a breaker is
performed before closing the breaker, in order to minimize internal damage that can occur due to the voltage difference,
both in magnitude and angle. This is extremely important in steam generating plants, where reclosing output lines with
angle differences can lead to severe damage to the turbine axis.
Figure 5-23: Synchromism check element
The difference in voltage level and phase angle in a given moment is the result of the existing load between remote
sources connected through parallel circuits (load flux), as well as a consequence of the impedance of those elements
connecting them (even if there is no load flux in parallel circuits, or because sources to be connected are completely
independent and isolated from one another).
In interconnected systems, the angle difference between both ends of an open breaker is usually negligible, as its sources
are remotely connected through other elements (equivalent or parallel circuits). However, in isolated circuits as in the case
of an independent generator, the difference in angle, voltage levels and relative slip of voltage phasors can be very
important. It may happen that the relative slip of voltage values is very low or null so that they are rarely in phase. Luckily,
due to the changing conditions of a power system (connection-disconnection of loads, sources, and new inductive-
capacitive elements) the relative slip between phasors is not null and they can be synchronized.
In the first case, even if we must take into consideration the length of the line whose ends (sources) are connected for
determining the angle difference between them, this is not enough to fix the synchronism conditions before closing the
breaker. Experience tells us that the window of angle difference between voltage phasors must be fixed to a value of 15º-
20º.
WARNING
When testing this function do not forget that the relay must detect an open breaker to operate.
V
s
V
r
C/2
Z
line
C/2
25
Z
Parallel
52
s
52
r
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...