CHAPTER 5: SETPOINTS
5.3 SYSTEM SETUP
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-31
5.3 System setup
This section shows the settings related to the system setup definition.
5.3.1 General settings
This section determines the settings of the element configuration regarding its connection to the power system.
The system rated voltage is used as reference by the voltage restraint in the phase timed overcurrent element.
The Frequency reference marks the voltage channel to which the system Frequency is measured.
The auxiliary voltage setting can be selected between VN and VX.
VN means that all elements using neutral voltage take the value directly from the fourth voltage input.
VX means that all elements using neutral voltage take the value calculated from phase voltages.
5.3.2 Miscellaneous settings
This section determines the relays status configuration regarding the service and local or remote modes.
5.3.2.1 Out of service setting
The unit
Relay Out of Service
setting is configured in
Setpoint > System Setup > Miscellaneous
. The unit also has an
Out
of Service
status that is configured in
Relay configuration > Protection elements
. When active, these states stop all
changes to PLC equations and functions, including changes in the input/output boards, so if there is a change in any input
Setpoint > System Setup > General settings
setting Description
Name
Default Value
Step
Range
Phase CT ratio
Phase CT Ratio
1.0
0.1
[1.0 : 6000.0]
Ground CT ratio
Ground CT Ratio
1.0
0.1
[1.0 : 6000.0]
Sensitive ground CT ratio
Stv Ground CT Ratio
1.0
0.1
[1.0 : 6000.0]
Phase VT ratio
Phase VT Ratio
1.0
0.1
[1.0 : 6000.0]
Phase VT connection
Phase VT Connection
WYE
N/A
[WYE – DELTA]
Rated voltage
Nominal Voltage
100.0
0.1
[1.0 : 250.0]
Rated Frequency
Nominal Frequency
50 Hz
N/A
[50-60]
Phase rotation
Phase Rotation
ABC
N/A
[ABC – ACB]
Frequency reference
Frequency Reference
VI
N/A
[VI-VII-VIII]
Auxiliary Voltage
Auxiliary Voltage
VX
N/A
[VX – VN]
Snapshot Event generation
Snapshot Events
DISABLED
N/A
[DISABLED – ENABLED]
Primary Meter Units
Primary Meter Units
KA_KV
N/A
[KA_KV; A_V]
Device Name
Device Name
N/A
Setpoint > System Setup > MISCELLANEOUS settings
setting Description
Name
Default Value
Step
Range
Relay Out of Service
Relay Out of Service
ENABLED
N/A
[DISABLED – ENABLED]
Local/Remote Blocked
Local/Remote Blocked
OFF
N/A
[ON -OFF]
Active Language
Active Language
0
N/A
[0;1]
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...