CHAPTER 5: SETPOINTS
5.4 PROTECTION ELEMENTS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-85
Table 5-56: 59NH/59NL element settings
The snapshot event setting enables or disables the snapshot event generation for this element.
5.4.8.4 Negative sequence overvoltage element (47)
The Negative sequence phase overvoltage element uses as its input magnitude the negative sequence component
calculated from the phase voltage values. This element can be used to detect the loss of one or two phases, unbalance
voltage conditions, etc.
Table 5-57: 47 element settings
The snapshot event setting enables or disables the snapshot event generation for this element.
5.4.8.5 Auxiliary overvoltage element (59X)
This is an Auxiliary overvoltage element for general use that uses as its input magnitude the voltage measured by the 4
th
VT (when VX is selected as Auxiliary Voltage in General Settings). The time delay for element 59X can be set from 0 to 900
seconds. The element has a reset than can be programmed from 0 to 900 seconds.
Table 5-58: 59X element settings
The snapshot event setting enables or disables the snapshot event generation for this element.
SETPOINT > PROTECTION ELEMENT > SETTING GROUP X > Voltage Elements >
>Neutral OV High > Neutral OV High 1> Neutral OV High 2 > Neutral OV High 3
>Neutral OV Low > Neutral OV Low 1> Neutral OV Low 2 > Neutral OV Low 3
setting Description
Name
Default Value
Step
Range
Function permission
Function
DISABLED
N/A
[DISABLED – ENABLED]
Pickup Level
Pickup Level
10
1 V
[3 : 300 ]
Trip time
Trip Delay
10.00
0.01 s
[0.00 : 900.00]
Reset time
Reset Delay
0.00
0.01 s
[0.00 : 900.00]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
SETPOINT > PROTECTION ELEMENT > SETTING GROUP X > VOLTAGE ELEMENTS > Negative Sequence OV >
Negative Sequence OV 1> Negative Sequence OV 2 > Negative Sequence OV 3
setting Description
Name
Default Value
Step
Range
Function permission
Function
DISABLED
N/A
[DISABLED – ENABLED]
Pickup Level
Pickup Level
10
1 V
[3 : 300]
Trip time
Trip Delay
10.00
0.01 s
[0.00 : 900.00]
Reset time
Reset Delay
0.00
0.01 s
[0.00 : 900.00]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
SETPOINT > PROTECTION ELEMENT > SETTING GROUP X > VOLTAGE ELEMENTS > Auxiliary OV >
Auxiliary OV 1> Auxiliary OV 2 > Auxiliary OV 3
setting Description
Name
Default Value
Step
Range
Function permission
Function
DISABLED
N/A
[DISABLED – ENABLED]
Pickup Level
Pickup Level
10
1 V
[3 : 300]
Trip time
Trip Delay
10.00
0.01 s
[0.00 : 900.00]
Reset time
Reset Delay
0.00
0.01 s
[0.00 : 900.00]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...