APPENDIX C: DNP 3.0 PROTOCOL FOR F650
C.3 IMPLEMENTATION TABLE
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
c-9
IMPLEMENTATION TABLE (Sheet 2 out of 3)
Note 1: A default variation refers to the variation responded when variation 0 is requested and/or in class 0, 1, 2, or 3 scans.
Note 2: For static (non-change-event) objects, qualifiers 17 or 28 are only responded when a request is sent with qualifiers 17 or 28,
respectively. Otherwise, static object requests sent with qualifiers 00, 01, 06, 07, or 08, are responded to with qualifiers 00 or 01 (for
change-event objects, qualifiers 17 or 28 are always responded).
Note 3: Cold restarts are implemented the same as warm restarts – The F650 is not restarted, but the DNP process is restarted.
OBJECT
REQUEST
RESPONSE
Object
No.
Variation
No.
Description
Function Codes
(dec)
Qualifier Codes (hex) Function Codes Qualifier Codes
(hex)
21
0
Frozen Counter - All Variations
1
(read)
06
(no range, or all)
22
0
Counter Change Event - All
Variations
1
(read)
06
(no range, or all)
07,08
(limited qty)
23
0
Frozen Counter Change Event
1
(read)
06
(no range, or all)
07,08
(limited qty)
30
0
Analog Input - All Variations
1
(read)
22
(assign class)
06
(no range, or all)
00,01
(start-stop)
07,08
(limited qty)
17,28
(index)
30
1
32-Bit Analog Input
See Note 1
1
(read)
22
(assign class)
000,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
129
(response)
00, 01
(start-
stop)
17,28
(index)
See Note 2
30
2
16-Bit Analog Input
1
(read)
22
(assign class)
00,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
129
(response)
00, 01
(start-
stop)
17,28
(index)
See Note 2
30
3
32-Bit Analog Input without Flag
1
(read)
22
(assign class)
00,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
129
(response)
00, 01
(start-
stop)
17,28
(index)
See Note 2
30
4
16-Bit Analog Input without Flag
1
(read)
22
(assign class)
00,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
129
(response)
00, 01
(start-
stop)
17,28
(index)
See Note 2
30
5
Analog Short Float
1
(read)
22
(assign class)
00,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
129
(response)
00, 01
(start-
stop)
17,28
(index)
See Note 2
32
0
Analog Change Event - All Variations 1
(read)
06
(no range, or all)
07,08
(limited qty)
32
1
32-Bit Analog Change Event without
Time
See Note 1
1
(read)
06
(no range, or all)
07,08
(limited qty)
129
(response)
130
(unsol.resp)
17, 28
(index)
32
2
16-Bit Analog Change Event without
Time
1
(read)
06
(no range, or all)
07,08
(limited qty)
129
(response)
130
(unsol.resp)
17, 28
(index)
32
3
32-Bit Analog Change Event with
Time
1
(read)
06
(no range, or all)
07,08
(limited qty)
129
(response)
130
(unsol.resp)
17,28
(index)
32
4
16-Bit Analog Change Event with
Time
1
(read)
06
(no range, or all)
07,08
(limited qty)
129
(response)
130
(unsol.resp)
17,28
(index)
32
5
Analogs (Short-float) without time
1
(read)
06
(no range, or all)
07,08
(limited qty)
129
(response)
130
(unsol.resp)
17,28
(index)
32
7
Analogs (Short-float) with time
1
(read)
06
(no range, or all)
07,08
(limited qty)
129
(response)
130
(unsol.resp)
17,28
(index)
34
0
Analog Input Reporting Deadband
1
(read)
00,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
34
1
16-Bit Analog Input Reporting
Deadband
See Note 1
1
(read)
00,01
(start-stop)
06
(no range, or all)
07,08
(limited qty)
17,28
(index)
129
(response)
00,01
(start-
stop)
17,28
(index)
See Note 2
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...