10.2 OUT OF SERVICE SETTING
CHAPTER 10: COMMISSIONING
10.2 Out of service setting
The
Relay Out Of Service
setting is configured in
Setpoint > System Setup > Miscellaneous
. The unit also has an
Out of
Service
status that is configured in
Relay configuration > Protection elements
. When active, these states stop all
changes to PLC equations and functions, including changes to the input/output boards, so if there is a change in any input
or output the unit will not show this change until it has returned to ready mode. For example if an output is closed and the
unit goes to the
Out of Service
state, the output is kept closed even if the state that closed it changes and would otherwise
open the output. When the unit goes out of the
Out of Service
state, the output is then opened.
When the
Out of Service
status goes to ON, or the setting has been changed to Enabled, the ready LED also changes to
red. Be careful if ready LED is linked to an output, because the output will not change its state. To set outputs to ready
state see factory default Logic & Configuration in the detailed manual. Take notice that, in the default configuration, the
general setting out of service is enabled, so it is necessary to change to disabled to start working with the unit
The following figure shows the flow chart of these states
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...