CHAPTER 5: SETPOINTS
5.5 CONTROL ELEMENTS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-125
The analog level value is by default in a reset state, when the value meets the comparison (inside or outside the
comparison band) the "Analog Level X" signal is activated if the analog value remains active the time set in the analog
delay setting. When the activation conditions are not met the "Analog Level X" value goes to the reset state.
An analog change must remain active at least 40 ms to be considered, plus the analog time setting. Besides the snapshot
event data has a 20 ms accuracy.
5.5.8 Maximum number of starts (66)
For F650 with firmware version below 7.XX, the special model F650 MOD003 relay incorporates a maximum number of
starts function (66) to prevent operators from jogging the motor (multiple starts and stops performed in rapid succession).
For F650 with firmware version 7.XX this element is included in standard models (No special model (MOD) is required)
A motor start is assumed to be occurring when the F650 measures the transition of the motor current from below 5% of
FLA to some value above 7% of FLA. Breaker status can also be used to detect motor starts. At this point, one of the Starts/
Hour timers is loaded with 60 minutes. Even unsuccessful start attempts are logged as starts for this feature. Once the
motor is stopped, the number of starts within the past hour is compared to the number of starts allowable. If the two
numbers are the same, a block occurs. If a block occurs, the lockout time is equal to the longest time elapsed since a start
within the past hour, subtracted from one hour.
Analog Level 02
Analog Level 03
Analog Level 04
Analog Level 05
Analog Level 06
Analog Level 07
Analog Level 08
Analog Level 09
Analog Level 10
Analog Level 11
Analog Level 12
Analog Level 13
Analog Level 14
Analog Level 15
Analog Level 16
Analog Level 17
Analog Level 18
Analog Level 19
Analog Level 20
technical characteristics
Metering algorithm
Fundamental
Tripping time accuracy
±250 ms or 5% whichever is greater
Full load Amps
0.5 to 10.0 A in steps of 0.1
Breaker supervision
Selectable by settings
Min. Stop time
0.0 to 900.0s in steps of 0.1
Number of starts
0 to 10 in steps of 1
Time to restart
0 to 100 minutes in steps of 1
Reset Counter
Selectable by settings
Snapshot events
Selectable by settings
Operate time
<45ms at 50Hz, typically
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...