CHAPTER 10: COMMISSIONING
10.9 INPUTS AND OUTPUTS
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
10-9
10.9 Inputs and outputs
During all tests, the screw on the rear of the relay must be grounded.
10.9.1 Digital inputs
During this test, the user determines the activation/deactivation points for every input in the relay for the set voltage value
of 30 Volts.
Verify that the error does not exceed ± 10% (+10% on activation, -10% on deactivation).
Default board settings for the input test can be modified in EnerVista 650 Setup software in:
Setpoint > Inputs/Outputs > Contact I/O > Board X
X, is substituted by the corresponding board:
F for board in first slot
G for board in second slot
H for board in first slot of CIO module
J for board in second slot of CIO module
Test settings for mixed board (type 1:16 inputs and 8 outputs):
The inputs test is completed by groups of 8 inputs, as this type of board has 2 groups of 8 inputs with the same common.
For the first 8 inputs, the voltage threshold setting is determined by Voltage Threshold A. For the next 8 inputs, the setting
is Voltage Threshold B. Inputs (or contact converters, CC1 – CC16) must also be set to POSITIVE.
Test settings for mixed board (type 2: 8 digital inputs, 4 blocks for supervision and 8 outputs):
The inputs test is completed by groups of 4 inputs, as this type of board has 2 groups of 4 inputs with the same common.
For the first 4 inputs, the voltage threshold setting is determined by Voltage Threshold A. For the next 4 inputs, the setting
is Voltage Threshold B. Inputs (or contact converters, CC1 – CC8) must also be set to POSITIVE.
If the relay incorporates more input modules, these tests must also be applied to them.
I/O Board Type 1 (MIXED)
Voltage Threshold A_X
30 V
Voltage Threshold B_X
40 V
Debounce Time A_X
5 ms
Debounce Time B_X
5 ms
Input Type_X_CC1 (CC1)
POSITIVE
...
...
Input Type_X_CC16 (CC16)
POSITIVE
I/O Board Type 2 (SUPERVISION)
Voltage Threshold A_X
30 V
Voltage Threshold B_X
40 V
Debounce Time A_X
5 ms
Debounce Time B_X
5 ms
Input Type_X_CC1 (CC1)
POSITIVE
...
...
Input Type_X_CC8 (CC8)
POSITIVE
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...