5.9 RELAY CONFIGURATION
CHAPTER 5: SETPOINTS
5.9.3.1 Programming an operation
Example of how to program an operation to close a breaker with an operating time of 90 ms (closing), incorporating 52/b
contacts to indicate the change of position, using an interlock logic to enable the operation if there is synchronism
condition, and there is no autoreclose in progress. The operation must be commanded from the relay faceplate using one
of the available operation push buttons.
To configure the related operation, go to
Setpoint > Relay Configuration
and select
Operations
tab.
This screen shows all the fields required for the operations configuration in the F650. In order to select an operation, click
the operation name under the
Select
column, and all the related parameters are enabled. The chosen name for the
operation is entered in
Command Text
. To configure an interlock logic, select the
Logic
option in
Interlocks Type
. Once this
option has been selected, the interlock configuration screen is enabled. To display this screen, click
Press for Logic
for the
desired operation on the
Interlocks
column. On this
Interlocks
screen, the two conditions that conform the Interlock that
enables the operation have been selected. To save the interlock, click the disk icon on the toolbar. A
Logic Saved
displays.
Once the Interlocks have been defined, the user must define the success conditions for the operation, define
Final State
Type
as LOGIC, and a PRESS FOR LOGIC message lights up below
Final States
. When clicking PRESS FOR LOGIC, the
success condition screen is displayed, defining there as BREAKER CLOSED.
The front key to be used for executing the Operation can be selected on the Frontal Key column, in this example the
Key I
option is selected on
Frontal Key
. As none of the other contact input or virtual output options are going to be used they are
set to
None
. The success condition time
Time out
is set to
500 ms
, and the operation is only enabled through the relay
keypad, so only the
MMI
option is selected, thus disabling the rest of options (COM1, COM2, ETHERNET master are not
selected).
All the selections previously related are summarized in the following table:
Table 5-92: Operation settingSs
Finally, configure a contact output to be activated with the programmed Operation (Operation1).
OPERATION
COMMAND TEXT
settingS
VALUE/SOURCE
Operation1
CLOSE BREAKER
INTERLOCK (LOGIC)
SYNCHK CLOSE PERM
FINAL STATES (LOGIC)
BREAKER CLOSED
FRONT KEY
I Key
INPUT
Not configured
VIRTUAL OUTPUT
Not configured
TIMEOUT
500
CHANNELS
MMI
Summary of Contents for F650
Page 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Page 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Page 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Page 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Page 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Page 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...