![GE Grid Solutions F60 Instruction Manual Download Page 717](http://html.mh-extra.com/html/ge-grid-solutions/f60/f60_instruction-manual_571876717.webp)
GE Multilin
F60 Feeder Protection System
F-11
APPENDIX F
F.2 DNP POINT LISTS
F
F.2.4 ANALOG INPUTS
The DNP analog input data points are configured through the
PRODUCT SETUP
COMMUNICATIONS
DNP / IEC104 POINT
LISTS
ANALOG INPUT / MME POINTS
menu. See the
Communications
section of Chapter 5 for details.
It is important to note that 16-bit and 32-bit variations of analog inputs are transmitted through DNP as signed numbers.
Even for analog input points that are not valid as negative values, the maximum positive representation is 32767 for 16-bit
values and 2147483647 for 32-bit values. This is a DNP requirement.
The deadbands for all Analog Input points are in the same units as the Analog Input quantity. For example, an Analog Input
quantity measured in volts has a corresponding deadband in units of volts. This is in conformance with DNP Technical Bul-
letin 9809-001: Analog Input Reporting Deadband. Relay settings are available to set default deadband values according to
data type. Deadbands for individual Analog Input Points can be set using DNP Object 34.
Static (Steady-State) Object Number:
30
Change Event Object Number:
32
Request Function Codes supported:
1 (read), 2 (write, deadbands only), 22 (assign class)
Static Variation reported when variation 0 requested:
1 (32-Bit Analog Input)
Change Event Variation reported when variation 0 requested:
1 (Analog Change Event without Time)
Change Event Scan Rate: defaults to
500 ms
Change Event Buffer Size:
256
Default Class for all Points:
2
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...