6206
Autoreclose 1 Manual Close
0 to 4294967295
---
1
F300
0
6208
Autoreclose 1 Manual Reset from LO
0 to 4294967295
---
1
F300
0
620A
Autoreclose 1 Reset Lockout if Breaker Closed
0 to 1
---
1
F108
0 (Off)
620B
Autoreclose 1 Reset Lockout On Manual Close
0 to 1
---
1
F108
0 (Off)
620C
Autoreclose 1 Breaker Closed
0 to 4294967295
---
1
F300
0
620E
Autoreclose 1 Breaker Open
0 to 4294967295
---
1
F300
0
6210
Autoreclose 1 Block Time Upon Manual Close
0 to 655.35
s
0.01
F001
1000
6211
Autoreclose 1 Dead Time Shot 1
0 to 655.35
s
0.01
F001
100
6212
Autoreclose 1 Dead Time Shot 2
0 to 655.35
s
0.01
F001
200
6213
Autoreclose 1 Dead Time Shot 3
0 to 655.35
s
0.01
F001
300
6214
Autoreclose 1 Dead Time Shot 4
0 to 655.35
s
0.01
F001
400
6215
Autoreclose 1 Reset Lockout Delay
0 to 655.35
s
0.01
F001
6000
6216
Autoreclose 1 Reset Time
0 to 655.35
s
0.01
F001
6000
6217
Autoreclose 1 Incomplete Sequence Time
0 to 655.35
s
0.01
F001
500
6218
Autoreclose 1 Events
0 to 1
---
1
F102
0 (Disabled)
6219
Autoreclose 1 Reduce Max 1
0 to 4294967295
---
1
F300
0
621B
Autoreclose 1 Reduce Max 2
0 to 4294967295
---
1
F300
0
621D
Autoreclose 1 Reduce Max 3
0 to 4294967295
---
1
F300
0
621F
Autoreclose 1 Add Delay 1
0 to 4294967295
---
1
F300
0
6221
Autoreclose 1 Delay 1
0 to 655.35
s
0.01
F001
0
6222
Autoreclose 1 Add Delay 2
0 to 4294967295
---
1
F300
0
6224
Autoreclose 1 Delay 2
0 to 655.35
s
0.01
F001
0
6225
Reserved (4 items)
0 to 0.001
---
0.001
F001
0
6229
...Repeated for Autoreclose 2
Negative Sequence Time Overcurrent (Read/Write Grouped Setting) (2 modules)
6300
Negative Sequence Time Overcurrent 1 Function
0 to 1
---
1
F102
0 (Disabled)
6301
Negative Sequence Time Overcurrent 1 Signal Source
0 to 5
---
1
F167
0 (SRC 1)
6302
Negative Sequence Time Overcurrent 1 Pickup
0 to 30
pu
0.001
F001
1000
6303
Negative Sequence Time Overcurrent 1 Curve
0 to 16
---
1
F103
0 (IEEE Mod Inv)
6304
Negative Sequence Time Overcurrent 1 Multiplier
0 to 600
---
0.01
F001
100
6305
Negative Sequence Time Overcurrent 1 Reset
0 to 1
---
1
F104
0 (Instantaneous)
6306
Negative Sequence Time Overcurrent 1 Block
0 to 4294967295
---
1
F300
0
6308
Negative Sequence Time Overcurrent 1 Target
0 to 2
---
1
F109
0 (Self-reset)
6309
Negative Sequence Time Overcurrent 1 Events
0 to 1
---
1
F102
0 (Disabled)
630A
Reserved (7 items)
0 to 1
---
1
F001
0
6311
...Repeated for Negative Sequence Time Overcurrent 2
Negative Sequence Instantaneous Overcurrent (Read/Write Grouped Setting) (2 modules)
63C0
Negative Sequence Instantaneous OC 1 Function
0 to 1
---
1
F102
0 (Disabled)
63C1
Negative Sequence Instantaneous OC 1 Signal Source
0 to 5
---
1
F167
0 (SRC 1)
63C2
Negative Sequence Instantaneous Overcurrent 1 Pickup
0 to 30
pu
0.001
F001
1000
63C3
Negative Sequence Instantaneous Overcurrent 1 Delay
0 to 600
s
0.01
F001
0
63C4
Negative Sequence Instantaneous OC 1 Reset Delay
0 to 600
s
0.01
F001
0
63C5
Negative Sequence Instantaneous Overcurrent 1 Block
0 to 4294967295
---
1
F300
0
63C7
Negative Sequence Instantaneous Overcurrent 1 Target
0 to 2
---
1
F109
0 (Self-reset)
63C8
Negative Sequence Instantaneous Overcurrent 1 Events
0 to 1
---
1
F102
0 (Disabled)
63C9
Reserved (8 items)
0 to 1
---
1
F001
0
63D1
...Repeated for Negative Sequence Instantaneous OC 2
Negative Sequence Overvoltage (Read/Write Grouped Setting) (3 modules)
6440
Negative Sequence Overvoltage 1 Function
0 to 1
---
1
F102
0 (Disabled)
6441
Negative Sequence Overvoltage 1 Source
0 to 5
---
1
F167
0 (SRC 1)
6442
Negative Sequence Overvoltage 1 Pickup
0 to 1.25
pu
0.001
F001
300
6443
Negative Sequence Overvoltage 1 Pickup Delay
0 to 600
s
0.01
F001
50
6444
Negative Sequence Overvoltage 1 Reset Delay
0 to 600
s
0.01
F001
50
6445
Negative Sequence Overvoltage 1 Block
0 to 4294967295
---
1
F300
0
Table B–10: MODBUS MEMORY MAP (Sheet 34 of 70)
ADDR
REGISTER NAME
RANGE
UNITS
STEP
FORMAT
DEFAULT
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...