5.4 SYSTEM SETUP
5
c) PMU CALIBRATION
PATH: SETTINGS
SYSTEM SETUP
PHASOR MEASUREMENT UNIT
PHASOR MEASUREMENT UNIT 1
PMU 1 CALIBRA-
TION
This menu contains user angle and magnitude calibration data for the phasor measurement unit (PMU). This data is com-
bined with the factory adjustments to shift the phasors for better accuracy.
•
PMU 1 VA... IG CALIBRATION ANGLE
: These settings recognize applications with protection class voltage and cur-
rent sources, and allow the user to calibrate each channel (four voltages and four currents) individually to offset errors
introduced by VTs, CTs, and cabling. The setting values are effectively added to the measured angles. Therefore, enter
a positive correction of the secondary signal lags the true signal; and negative value if the secondary signal leads the
true signal.
PMU 1
CALIBRATION
PMU 1 VA CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 VA CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 VB CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 VB CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 VC CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 VC CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 VX CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 VX CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 IA CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 IA CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 IB CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 IB CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 IC CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 IC CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 IG CALIBRATION
ANGLE: 0.00°
Range: –5.00 to 5.00° in steps of 0.05
MESSAGE
PMU 1 IG CALIBRATION
MAG: 100.0%
Range: 95.0 to 105.0 in steps of 0.1%
MESSAGE
PMU 1 SEQ VOLT SHIFT
ANGLE: 0°
Range: –180 to 180° in steps of 30
MESSAGE
PMU 1 SEQ CURR SHIFT
ANGLE: 0°
Range: –180 to 180° in steps of 30
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...