GE Multilin
F60 Feeder Protection System
5-59
5 SETTINGS
5.2 PRODUCT SETUP
5
The settings menu for the fast EGD exchange is shown below:
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
EGD PROTOCOL
FAST PROD EXCH 1 CONFIGURATION
Fast exchanges (50 to 1000 ms) are generally used in control schemes. The F60 has one fast exchange (exchange 1) and
two slow exchanges (exchange 2 and 3).
The settings menu for the slow EGD exchanges is shown below:
PATH: SETTINGS
PRODUCT SETUP
COMMUNICATIONS
EGD PROTOCOL
SLOW PROD EXCH 1(2) CONFIGURATION
Slow EGD exchanges (500 to 1000 ms) are generally used for the transfer and display of data items. The settings for the
fast and slow exchanges are described below:
•
EXCH 1 DESTINATION
: This setting specifies the destination IP address of the produced EGD exchange. This is usu-
ally unicast or broadcast.
•
EXCH 1 DATA RATE
: This setting specifies the rate at which this EGD exchange is transmitted. If the setting is 50 ms,
the exchange data will be updated and sent once every 50 ms. If the setting is 1000 ms, the exchange data will be
updated and sent once per second. EGD exchange 1 has a setting range of 50 to 1000 ms. Exchanges 2 and 3 have a
setting range of 500 to 1000 ms.
FAST PROD EXCH 1
CONFIGURATION
EXCH 1 FUNCTION:
Disable
Range: Disable, Enable
MESSAGE
EXCH 1 DESTINATION:
0.0.0.0
Range: standard IP address
MESSAGE
EXCH 1 DATA RATE:
1000 ms
Range: 50 to 1000 ms in steps of 1
MESSAGE
EXCH 1 DATA ITEM 1:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range)
MESSAGE
EXCH 1 DATA ITEM 2:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range)
MESSAGE
EXCH 1 DATA ITEM 3:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range)
↓
MESSAGE
EXCH 1 DATA ITEM 20:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range)
SLOW PROD EXCH 1
CONFIGURATION
EXCH 1 FUNCTION:
Disable
Range: Disable, Enable
MESSAGE
EXCH 1 DESTINATION:
0.0.0.0
Range: standard IP address
MESSAGE
EXCH 1 DATA RATE:
1000 ms
Range: 500 to 1000 ms in steps of 1
MESSAGE
EXCH 1 DATA ITEM 1:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range in decimal)
MESSAGE
EXCH 1 DATA ITEM 2:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range in decimal)
MESSAGE
EXCH 1 DATA ITEM 3:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range in decimal)
↓
MESSAGE
EXCH 1 DATA ITEM 50:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range in decimal)
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...