GE Multilin
F60 Feeder Protection System
5-81
5 SETTINGS
5.2 PRODUCT SETUP
5
When in the Disabled mode, minor alarms do not assert a FlexLogic operand, write to the event recorder, or display target
messages. Moreover, they do not trigger the
ANY MINOR ALARM
or
ANY SELF-TEST
messages. When in Enabled mode,
minor alarms continue to function along with other major and minor alarms. See the
Relay Self-tests
section in chapter 7 for
information on major and minor self-test alarms.
5.2.13 CONTROL PUSHBUTTONS
PATH: SETTINGS
PRODUCT SETUP
CONTROL PUSHBUTTONS
CONTROL PUSHBUTTON 1(7)
There are three standard control pushbuttons, labeled USER 1, USER 2, and USER 3, on the standard and enhanced front
panels. These are user-programmable and can be used for various applications such as performing an LED test, switching
setting groups, and invoking and scrolling though user-programmable displays.
Firmware revisions 3.2x and older use these three pushbuttons for manual breaker control. This functionality has been
retained – if the breaker control feature is configured to use the three pushbuttons, they cannot be used as user-program-
mable control pushbuttons.
The location of the control pushbuttons are shown in the following figures.
Figure 5–11: CONTROL PUSHBUTTONS (ENHANCED FACEPLATE)
An additional four control pushbuttons are included on the standard faceplate when the F60 is ordered with the 12 user-pro-
grammable pushbutton option.
Figure 5–12: CONTROL PUSHBUTTONS (STANDARD FACEPLATE)
Control pushbuttons are not typically used for critical operations and are not protected by the control password. However,
by supervising their output operands, the user can dynamically enable or disable control pushbuttons for security reasons.
Each control pushbutton asserts its own FlexLogic operand. These operands should be configured appropriately to perform
the desired function. The operand remains asserted as long as the pushbutton is pressed and resets when the pushbutton
is released. A dropout delay of 100 ms is incorporated to ensure fast pushbutton manipulation will be recognized by various
features that may use control pushbuttons as inputs.
CONTROL
PUSHBUTTON 1
CONTROL PUSHBUTTON 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
CONTROL PUSHBUTTON 1
EVENTS: Disabled
Range: Disabled, Enabled
Control pushbuttons
842813A1.CDR
842733A2.CDR
PICKUP
ALARM
TRIP
TEST MODE
TROUBLE
IN SERVICE
STATUS
USER 3
USER 2
USER 1
RESET
EVENT CAUSE
NEUTRAL/GROUND
PHASE C
PHASE B
PHASE A
OTHER
FREQUENCY
CURRENT
VOLTAGE
THREE
STANDARD
CONTROL
PUSHBUTTONS
USER 7
USER 6
USER 5
USER 4
FOUR EXTRA
OPTIONAL
CONTROL
PUSHBUTTONS
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...