7 COMMANDS AND TARGETS
7.1 COMMANDS
7
sured signals are raw inputs to the PMU under test, their independently captured record, processed using third-party soft-
ware, is a good reference point for accuracy calculations. Such a record proves useful when discussing the test results, and
should be retained as a part of the testing documentation.
Note that the PMU under such test does not have to be connected to a real GPS receiver as the accuracy is measured with
respect to the timing reference provided to the PMU and not to the absolute UTC time. Therefore a simple IRIG-B genera-
tor could be used instead. Also, the test set does not have to support GPS synchronization. Any stable signal source can
be used. If both the PMU under test and the test set use the timing reference, they should be driven from the same IRIG-B
signal: either the same GPS receiver or IRIG-B generator. Otherwise, the setpoints of the test set and the PMU measure-
ments should not be compared as they are referenced to different time scales.
Figure 7–2: USING THE PMU ONE-SHOT FEATURE TO TEST SYNCHROPHASOR MEASUREMENT ACCURACY
COLLECTING SYNCHRONIZED MEASUREMENTS
AD HOC
:
The one-shot feature can be used for ad hoc collection of synchronized measurements in the network. Two or more PMU
can be pre-scheduled to freeze their measurements at the same time. When frozen the measurements could be collected
using EnerVista UR Setup or a protocol client.
7.1.7 SECURITY
i
PATH: COMMANDS
SECURITY
With the CyberSentry option, this setting is available to enable or disable the following commands:
•
Administrator Logoff:
Selecting ‘Yes’ allows the Supervisor to forcefully logoff an administrator session.
•
Engineer Logoff:
Selecting ‘Yes’ allows the Supervisor to forcefully logoff an engineer session.
•
Operator Logoff:
Selecting ‘Yes’ allows the Supervisor to forcefully logoff an operator session.
•
Clear Security Data
: Selecting ‘Yes’ allows the Supervisor to forcefully clear all the security logs and clears all the
operands associated with the self-tests.
Targets
SECURITY
ADMINISTRATOR
LOGOFF: No
Range: Yes, No
Default: No
ENGINEER
LOGOFF: No
Range: Yes, No
Default: No
OPERATOR
LOGOFF: No
Range: Yes, No
Default: No
CLEAR SECURITY DATA:
Range: Yes, No
Default: No
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...