5 SETTINGS
5.7 CONTROL ELEMENTS
5
tion is declared in the corresponding phase and the
BRK RESTRIKE 1 OP
operand is asserted for a short period of time. The
user can add counters and other logic to facilitate the decision making process as to the appropriate actions upon detecting
a single restrike or a series of consecutive restrikes.
A restrike event (FlexLogic operand) is declared if all of the following hold:
•
The current is initially interrupted
•
The breaker status is open
•
An elevated high frequency current condition occurs (if the
BREAKER RESTRIKE 1 HF DETECT
setting is Enabled, other-
wise the condition is bypassed), and
•
The current subsequently drops out again
The algorithm is illustrated in the state machine diagram shown below.
Figure 5–127: ALGORITHM ILLUSTRATION – STATE MACHINE TO DETECT RESTRIKE
In this way, a distinction is made between a self-extinguishing restrike and permanent breaker failure condition. The latter
can be detected by the breaker failure function or a regular instantaneous overcurrent element. Also, a fast succession of
restrikes will be picked up by breaker failure or instantaneous overcurrent protection.
The following settings are available for each element.
•
BREAKER RESTRIKE 1 FUNCTION
: This setting enable and disables operation of the breaker restrike detection ele-
ment.
•
BRK RSTR 1 BLOCK
: This setting is used to block operation of the breaker restrike detection element.
•
BREAKER RESTRIKE 1 SOURCE
: This setting selects the source of the current for this element. This source must
have a valid CT bank assigned.
•
BREAKER RESTRIKE 1 PICKUP
: This setting specifies the pickup level of the overcurrent detector in per-unit values
of CT nominal current.
•
BREAKER RESTRIKE 1 RESET DELAY
: This setting specifies the reset delay for this element. When set to “0 ms”,
then FlexLogic operand will be picked up for only 1/8th of the power cycle.
Capacitor bank
offline
Current
interruption
(overcurrent)
High-frequency
elevated current
(if enabled)
Restrike detected:
OP state asserted
Breaker close
Breaker
close
Breaker
close
Capacitor bank
online
Current
interruption
(overcurrent)
Breaker open
command or breaker
open state
834768A2.CDR
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...