![GE Grid Solutions F60 Instruction Manual Download Page 533](http://html.mh-extra.com/html/ge-grid-solutions/f60/f60_instruction-manual_571876533.webp)
GE Multilin
F60 Feeder Protection System
A-11
APPENDIX A
A.1 PARAMETER LISTS
A
8213
SRC 2 Vc Harm[25]
%
Source 2 phase C voltage twenty-fifth harmonic
8672
Brk 1 Arc Amp A
kA
2
-cyc
Breaker 1 arcing amp phase A
8674
Brk 1 Arc Amp B
kA
2
-cyc
Breaker 1 arcing amp phase B
8676
Brk 1 Arc Amp C
kA
2
-cyc
Breaker 1 arcing amp phase C
8678
Brk 1 Op Time A
ms
Breaker 1 operating time phase A
8679
Brk 1 Op Time B
ms
Breaker 1 operating time phase B
8680
Brk 1 Op Time C
ms
Breaker 1 operating time phase C
8681
Brk 1 Op Time
ms
Breaker 1 operating time
8682
Brk 2 Arc Amp A
kA
2
-cyc
Breaker 2 arcing amp phase A
8684
Brk 2 Arc Amp B
kA
2
-cyc
Breaker 2 arcing amp phase B
8686
Brk 2 Arc Amp C
kA
2
-cyc
Breaker 2 arcing amp phase C
8688
Brk 2 Op Time A
ms
Breaker 2 operating time phase A
8689
Brk 2 Op Time B
ms
Breaker 2 operating time phase B
8690
Brk 2 Op Time C
ms
Breaker 2 operating time phase C
8691
Brk 2 Op Time
ms
Breaker 2 operating time
8784
HIZ Status
---
High impedance fault detection status
8785
HIZ Phase A Arc Conf
---
High impedance fault detection phase A arc confidence
8786
HIZ Phase B Arc Conf
---
High impedance fault detection phase B arc confidence
8787
HIZ Phase C Arc Conf
---
High impedance fault detection phase C arc confidence
8788
HIZ Neutral Arc Conf
---
High impedance fault detection neutral arc confidence
9024
Prefault Ia Mag [1]
Amps
Fault 1 pre-fault phase A current magnitude
9026
Prefault Ia Ang [1]
Degrees
Fault 1 pre-fault phase A current angle
9027
Prefault Ib Mag [1]
Amps
Fault 1 pre-fault phase B current magnitude
9029
Prefault Ib Ang [1]
Degrees
Fault 1 pre-fault phase B current angle
9030
Prefault Ic Mag [1]
Amps
Fault 1 pre-fault phase C current magnitude
9032
Prefault Ic Ang [1]
Degrees
Fault 1 pre-fault phase C current angle
9033
Prefault Va Mag [1]
Volts
Fault 1 pre-fault phase A voltage magnitude
9035
Prefault Va Ang [1]
Degrees
Fault 1 pre-fault phase A voltage angle
9036
Prefault Vb Mag [1]
Volts
Fault 1 pre-fault phase B voltage magnitude
9038
Prefault Vb Ang [1]
Degrees
Fault 1 pre-fault phase B voltage angle
9039
Prefault Vc Mag [1]
Volts
Fault 1 pre-fault phase C voltage magnitude
9041
Prefault Vc Ang [1]
Degrees
Fault 1 pre-fault phase C voltage angle
9042
Fault Ia Mag [1]
Amps
Fault 1 phase A current magnitude
9044
Fault Ia Ang [1]
Degrees
Fault 1 phase A current angle
9045
Fault Ib Mag [1]
Amps
Fault 1 phase B current magnitude
9047
Fault Ib Ang [1]
Degrees
Fault 1 phase B current angle
9048
Fault Ic Mag [1]
Amps
Fault 1 phase C current magnitude
9050
Fault Ic Ang [1]
Degrees
Fault 1 phase C current angle
9051
Fault Va Mag [1]
Volts
Fault 1 phase A voltage magnitude
9053
Fault Va Ang [1]
Degrees
Fault 1 phase A voltage angle
9054
Fault Vb Mag [1]
Volts
Fault 1 phase B voltage magnitude
9056
Fault Vb Ang [1]
Degrees
Fault 1 phase B voltage angle
9057
Fault Vc Mag [1]
Volts
Fault 1 phase C voltage magnitude
9059
Fault Vc Ang [1]
Degrees
Fault 1 phase C voltage angle
9060
Fault Type [1]
---
Fault 1 type
9061
Fault Location [1]
---
Fault 1 location
Table A–1: FLEXANALOG DATA ITEMS (Sheet 11 of 22)
ADDRESS
FLEXANALOG NAME
UNITS
DESCRIPTION
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...