MSVCB 1 SVENA:
The SV Stream Control is set by either toggling an assigned FlexLogic operand or a remote client
write, to start and stop the streaming of R-SV frames. If remote client control is disabled, a negative response is pro-
vided to the client in response to a write attempt. A FlexLogic operand (SvEna) is provided for each Aggregator that
reflects the state of the SvEna control where “1”= Enabled and “0”=Disabled. The logic for setting the SvEna control bit
is shown in the following figure.
Figure 5–53: LOGIC FOR SETTING SVENA CONTROL BIT
•
MSVCB 1 Client CONTRL:
This setting determines if a client can write to the reserve bit. When the assigned Flex-
Logic operand is a logic 1 state, remote clients can write to both the reserve bit and the SvEna bit. When the FlexLogic
operand is a logic 0 state, the remote client writes to the reserve bit, the SvEna is rejected by the UR, and a negative
response with the appropriate Service Error is returned to the client.
•
MSVCB 1 SVENA Default:
This setting sets the default state of the stream (On or Off) on power-up or restart.
•
MSVCB 1 CONFREV:
The relay increments the Configuration revision every time the configuration is changed. This
setting allows the user to reset the configuration back to 1 or a value from 1 to 4294967295.
•
MSVCB 1 PRIORITY:
A value from 0 through 7: The default value is 4.
•
MSVCB 1 IP Class:
The value represents the IPv4 Differentiated Services (formerly called TypeOfService) value. The
default value is set for Expedited Forwarding (101110B (46 or 2EH). This value provides priority routing, when sup-
ported in the routers.
•
MSVCB 1 VID:
A range of values limited from 0 to 4095.
•
MSVCB 1 APPID:
This setting allows the selection of a specific application ID for each sending device.
•
MSVCB 1 DEST IP Address:
This is the destination multicast address IP address that is entered in Standard IPV4
address format. The valid range for IPv4 is from 224.0.0.0 to 239.255.255.255, but the UR does not test the address
entered.
•
MSVCB 1 Security:
This setting selects the level of security and authentication used, as outlined in the following table,
and is in the form of an enumeration as per standard. The range is 0 to 2.
Shaded settings in the table are not supported in firmware 7.0.
MESSAGE
MSVCB 1 DEST. IP:
224.0.0.0
Range: 0 to 255.255.255.255
MESSAGE
MSVCB 1 SECURITY:
0
Range: 0 to 2
ENUMERATION
AUTHENTICATION
ENCRYPTION
0
no
no
Toggle Function
AND
AND
Positive
One-Shot
SvEna
Status
Pushbutton/
FlexOperand
(Momentary)
Write “0”
to SvEna
Write “1”
to SvEna
859739A1.cdr
NOTE
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...