5 SETTINGS
5.2 PRODUCT SETUP
5
This option is available when an INTER-RELAY COMMUNICATIONS card is specified at the time of order-
ing. With the option, direct inputs/outputs display by default. When you enable the teleprotection feature,
direct I/O is not visible.
Direct inputs and outputs are intended for exchange of status information (inputs and outputs) between UR-series relays
connected directly via type 7 or type 2 digital communications cards. The mechanism is very similar to IEC 61850 GSSE,
except that communications takes place over a non-switchable isolated network and is optimized for speed. On type 7
cards that support two channels, direct output messages are sent from both channels simultaneously. This effectively
sends direct output messages both ways around a ring configuration. On type 7 cards that support one channel, direct out-
put messages are sent only in one direction. Messages will be resent (forwarded) when it is determined that the message
did not originate at the receiver.
Direct output message timing is similar to GSSE message timing. Integrity messages (with no state changes) are sent at
least every 1000 ms. Messages with state changes are sent within the main pass scanning the inputs and asserting the
outputs unless the communication channel bandwidth has been exceeded. Two self-tests are performed and signaled by
the following FlexLogic operands:
1.
DIRECT RING BREAK
(direct input/output ring break). This FlexLogic operand indicates that direct output messages
sent from a UR-series relay are not being received back by the relay.
2.
DIRECT DEVICE 1 OFF to DIRECT DEVICE 16 OFF
(direct device offline). These FlexLogic operands indicate that direct
output messages from at least one direct device are not being received.
Direct input and output settings are similar to remote input and output settings. The equivalent of the remote device name
strings for direct inputs and outputs is the
DIRECT OUTPUT DEVICE ID
. The
DIRECT OUTPUT DEVICE ID
setting identifies the
relay in all direct output messages. All UR-series IEDs in a ring should have unique numbers assigned. The IED ID is used
to identify the sender of the direct input and output message.
If the direct input and output scheme is configured to operate in a ring (
DIRECT I/O CH1 RING CONFIGURATION
or
DIRECT I/O
CH2 RING CONFIGURATION
is “Yes”), all direct output messages should be received back. If not, the direct input/output ring
break self-test is triggered. The self-test error is signaled by the
DIRECT RING BREAK
FlexLogic operand.
Select the
DIRECT I/O DATA RATE
to match the data capabilities of the communications channel. All IEDs communicating
over direct inputs and outputs must be set to the same data rate. UR-series IEDs equipped with dual-channel communica-
tions cards apply the same data rate to both channels. Delivery time for direct input and output messages is approximately
0.2 of a power system cycle at 128 kbps and 0.4 of a power system cycle at 64 kbps, per each ‘bridge’.
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...