B-60
F60 Feeder Protection System
GE Multilin
B.4 MEMORY MAPPING
APPENDIX B
B
B0E8
IEC 61850 MMXU VAr.phsC Deadband 1
0.001 to 100
%
0.001
F003
10000
B0EA
IEC 61850 MMXU VA.phsA Deadband 1
0.001 to 100
%
0.001
F003
10000
B0EC
IEC 61850 MMXU VA.phsB Deadband 1
0.001 to 100
%
0.001
F003
10000
B0EE
IEC 61850 MMXU VA.phsC Deadband 1
0.001 to 100
%
0.001
F003
10000
B0F0
IEC 61850 MMXU PF.phsA Deadband 1
0.001 to 100
%
0.001
F003
10000
B0F2
IEC 61850 MMXU PF.phsB Deadband 1
0.001 to 100
%
0.001
F003
10000
B0F4
IEC 61850 MMXU PF.phsC Deadband 1
0.001 to 100
%
0.001
F003
10000
B0F6
...Repeated for Deadband 2
B12C
...Repeated for Deadband 3
B162
...Repeated for Deadband 4
B198
...Repeated for Deadband 5
B1CE
...Repeated for Deadband 6
IEC 61850 Received Analogs (Read Only) (32 modules)
B210
IEC 61850 Received Analog 1
-1000000000000 to
1000000000000
---
0.001
F060
0
B212
...Repeated for Received Analog 2
B214
...Repeated for Received Analog 3
B216
...Repeated for Received Analog 4
B218
...Repeated for Received Analog 5
B21A
...Repeated for Received Analog 6
B21C
...Repeated for Received Analog 7
B21E
...Repeated for Received Analog 8
B220
...Repeated for Received Analog 9
B222
...Repeated for Received Analog 10
B224
...Repeated for Received Analog 11
B226
...Repeated for Received Analog 12
B228
...Repeated for Received Analog 13
B22A
...Repeated for Received Analog 14
B22C
...Repeated for Received Analog 15
B22E
...Repeated for Received Analog 16
B230
...Repeated for Received Analog 17
B232
...Repeated for Received Analog 18
B234
...Repeated for Received Analog 19
B236
...Repeated for Received Analog 20
B238
...Repeated for Received Analog 21
B23A
...Repeated for Received Analog 22
B23C
...Repeated for Received Analog 23
B23E
...Repeated for Received Analog 24
B240
...Repeated for Received Analog 25
B242
...Repeated for Received Analog 26
B244
...Repeated for Received Analog 27
B246
...Repeated for Received Analog 28
B248
...Repeated for Received Analog 29
B24A
...Repeated for Received Analog 30
B24C
...Repeated for Received Analog 31
B24E
...Repeated for Received Analog 32
IEC 61850 Configurable Report Settings (Read/Write Setting)
B290
IEC 61850 Configurable Reports Dataset Items (64 items)
0 to 848
---
1
F615
0 (None)
Wattmetric Ground Fault Settings (Read/Write Grouped Setting) (2 modules)
B300
Wattmetric Ground Fault 1 Function
0 to 1
---
1
F102
0 (Disabled)
B301
Wattmetric Ground Fault 1 Source
0 to 5
---
1
F167
0 (SRC 1)
B302
Wattmetric Ground Fault 1 Voltage
0 to 1
---
1
F234
0 (Calculated VN)
B303
Wattmetric Ground Fault 1 Overvoltage Pickup
0.02 to 3.00
pu
0.01
F001
20
B304
Wattmetric Ground Fault 1 Current
0 to 1
---
1
F235
0 (Calculated IN)
Table B–10: MODBUS MEMORY MAP (Sheet 52 of 70)
ADDR
REGISTER NAME
RANGE
UNITS
STEP
FORMAT
DEFAULT
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...