![GE Grid Solutions F60 Instruction Manual Download Page 594](http://html.mh-extra.com/html/ge-grid-solutions/f60/f60_instruction-manual_571876594.webp)
B-50
F60 Feeder Protection System
GE Multilin
B.4 MEMORY MAPPING
APPENDIX B
B
8610
Breaker Failure 1 Timer 3 Pickup
0 to 65.535
s
0.001
F001
0
8611
Breaker Failure 1 Breaker Status 1 Phase A/3P
0 to 4294967295
---
1
F300
0
8613
Breaker Failure 1 Breaker Status 2 Phase A/3P
0 to 4294967295
---
1
F300
0
8615
Breaker Failure 1 Breaker Test On
0 to 4294967295
---
1
F300
0
8617
Breaker Failure 1 Phase Amp Hiset Pickup
0.001 to 30
pu
0.001
F001
1050
8618
Breaker Failure 1 Neutral Amp Hiset Pickup
0.001 to 30
pu
0.001
F001
1050
8619
Breaker Failure 1 Phase Amp Loset Pickup
0.001 to 30
pu
0.001
F001
1050
861A
Breaker Failure 1 Neutral Amp Loset Pickup
0.001 to 30
pu
0.001
F001
1050
861B
Breaker Failure 1 Loset Time
0 to 65.535
s
0.001
F001
0
861C
Breaker Failure 1 Trip Dropout Delay
0 to 65.535
s
0.001
F001
0
861D
Breaker Failure 1 Target
0 to 2
---
1
F109
0 (Self-reset)
861E
Breaker Failure 1 Events
0 to 1
---
1
F102
0 (Disabled)
861F
Breaker Failure 1 Phase A Initiate
0 to 4294967295
---
1
F300
0
8621
Breaker Failure 1 Phase B Initiate
0 to 4294967295
---
1
F300
0
8623
Breaker Failure 1 Phase C Initiate
0 to 4294967295
---
1
F300
0
8625
Breaker Failure 1 Breaker Status 1 Phase B
0 to 4294967295
---
1
F300
0
8627
Breaker Failure 1 Breaker Status 1 Phase C
0 to 4294967295
---
1
F300
0
8629
Breaker Failure 1 Breaker Status 2 Phase B
0 to 4294967295
---
1
F300
0
862B
Breaker Failure 1 Breaker Status 2 Phase C
0 to 4294967295
---
1
F300
0
862D
...Repeated for Breaker Failure 2
FlexState Settings (Read/Write Setting)
8800
FlexState Parameters (256 items)
0 to 4294967295
---
1
F300
0
Digital Elements (Read/Write Setting) (48 modules)
8A00
Digital Element 1 Function
0 to 1
---
1
F102
0 (Disabled)
8A01
Digital Element 1 Name
---
---
---
F203
“Dig Element 1“
8A09
Digital Element 1 Input
0 to 4294967295
---
1
F300
0
8A0B
Digital Element 1 Pickup Delay
0 to 999999.999
s
0.001
F003
0
8A0D
Digital Element 1 Reset Delay
0 to 999999.999
s
0.001
F003
0
8A0F
Digital Element 1 Block
0 to 4294967295
---
1
F300
0
8A11
Digital Element 1 Target
0 to 2
---
1
F109
0 (Self-reset)
8A12
Digital Element 1 Events
0 to 1
---
1
F102
0 (Disabled)
8A13
Digital Element 1 Pickup LED
0 to 1
---
1
F102
1 (Enabled)
8A14
Reserved (2 items)
---
---
---
F001
0
8A16
...Repeated for Digital Element 2
8A2C
...Repeated for Digital Element 3
8A42
...Repeated for Digital Element 4
8A58
...Repeated for Digital Element 5
8A6E
...Repeated for Digital Element 6
8A84
...Repeated for Digital Element 7
8A9A
...Repeated for Digital Element 8
8AB0
...Repeated for Digital Element 9
8AC6
...Repeated for Digital Element 10
8ADC
...Repeated for Digital Element 11
8AF2
...Repeated for Digital Element 12
8B08
...Repeated for Digital Element 13
8B1E
...Repeated for Digital Element 14
8B34
...Repeated for Digital Element 15
8B4A
...Repeated for Digital Element 16
8B60
...Repeated for Digital Element 17
8B76
...Repeated for Digital Element 18
8B8C
...Repeated for Digital Element 19
8BA2
...Repeated for Digital Element 20
8BB8
...Repeated for Digital Element 21
8BCE
...Repeated for Digital Element 22
Table B–10: MODBUS MEMORY MAP (Sheet 42 of 70)
ADDR
REGISTER NAME
RANGE
UNITS
STEP
FORMAT
DEFAULT
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...