5-208
F60 Feeder Protection System
GE Multilin
5.6 GROUPED ELEMENTS
5 SETTINGS
5
5.6.9 BREAKER FAILURE (ANSI 50BF/50NBF)
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
BREAKER FAILURE
BREAKER FAILURE 1(2)
BREAKER FAILURE 1
BF1 FUNCTION:
Disabled
Range: Disabled, Enabled
MESSAGE
BF1 MODE:
3-Pole
Range: 3-Pole, 1-Pole
MESSAGE
BF1 SOURCE:
SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
BF1 USE AMP SUPV:
Yes
Range: Yes, No
MESSAGE
BF1 USE SEAL-IN:
Yes
Range: Yes, No
MESSAGE
BF1 3-POLE INITIATE:
Off
Range: FlexLogic operand
MESSAGE
BF1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
BF1 PH AMP SUPV
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 N AMP SUPV
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 USE TIMER 1:
Yes
Range: Yes, No
MESSAGE
BF1 TIMER 1 PICKUP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BF1 USE TIMER 2:
Yes
Range: Yes, No
MESSAGE
BF1 TIMER 2 PICKUP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BF1 USE TIMER 3:
Yes
Range: Yes, No
MESSAGE
BF1 TIMER 3 PICKUP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BF1 BKR POS1
φ
A/3P:
Off
Range: FlexLogic operand
MESSAGE
BF1 BKR POS2
φ
A/3P:
Off
Range: FlexLogic operand
MESSAGE
BF1 BREAKER TEST ON:
Off
Range: FlexLogic operand
MESSAGE
BF1 PH AMP HISET
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 N AMP HISET
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
MESSAGE
BF1 PH AMP LOSET
PICKUP: 1.050 pu
Range: 0.001 to 30.000 pu in steps of 0.001
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...