5.4 SYSTEM SETUP
5 SETTINGS
5
•
PMU 1 CURR TRIGGER PICKUP
: This setting specifies the pickup threshold for the overcurrent trigger, in per unit of
the PMU source. A value of 1 pu is a nominal primary current. The comparator applies a 3% hysteresis.
•
PMU 1 CURR TRIGGER PKP TIME
: This setting can be used to filter out spurious conditions and avoid unnecessary
triggering of the recorder.
•
PMU 1 CURR TRIGGER DPO TIME
: This setting can be used to extend the trigger after the situation returned to nor-
mal. This setting is of particular importance when using the recorder in the forced mode (recording as long as the trig-
gering condition is asserted).
Figure 5–50: CURRENT TRIGGER SCHEME LOGIC
i) POWER TRIGGERING
PATH: SETTINGS
SYSTEM SETUP
PHASOR MEASUREMENT...
PMU 1 TRIGGERING
PMU 1 POWER TRIGGER
This element responds to abnormal power. Separate thresholds are provided for active, reactive, and apparent powers. In
terms of signaling its operation the element does not differentiate between the three types of power. The trigger responds to
the single-phase and three-phase power signals of the phasor measurement unit (PMU) source.
•
PMU 1 POWER TRIGGER ACTIVE
: This setting specifies the pickup threshold for the active power of the source. For
single-phase power, 1 pu is a product of 1 pu voltage and 1 pu current, or the product of nominal secondary voltage,
the VT ratio and the nominal primary current. For the three-phase power, 1 pu is three times that for a single-phase
power. The comparator applies a 3% hysteresis.
PMU 1 POWER
TRIGGER
PMU 1 POWER TRIGGER
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
PMU 1 POWER TRIGGER
ACTIVE: 1.250 pu
Range: 0.250 to 3.000 pu in steps of 0.001
MESSAGE
PMU 1 POWER TRIGGER
REACTIVE: 1.250 pu
Range: 0.250 to 3.000 pu in steps of 0.001
MESSAGE
PMU 1 POWER TRIGGER
APPARENT: 1.250 pu
Range: 0.250 to 3.000 pu in steps of 0.001
MESSAGE
PMU 1 POWER TRIGGER
PKP TIME: 0.10 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PMU 1 POWER TRIGGER
DPO TIME: 1.00 s
Range: 0.00 to 600.00 s in steps of 0.01
MESSAGE
PMU 1 PWR TRIG BLK:
Off
Range: FlexLogic operand
MESSAGE
PMU 1 POWER TRIGGER
TARGET: Self-Reset
Range: Self-Reset, Latched, Disabled
MESSAGE
PMU 1 POWER TRIGGER
EVENTS: Disabled
Range: Enabled, Disabled
SETTINGS
PMU 1 CURR TRIGGER
FUNCTION:
Enabled = 1
PMU 1 CURR TRIG BLK:
Off = 0
SETTINGS
PMU 1 SIGNAL
SOURCE:
AND
SETTINGS
PMU 1 CURR TRIGGER PICKUP:
RUN
SETTINGS
PMU 1 CURR TRIGGER DPO TIME:
t
DPO
FLEXLOGIC OPERAND
PMU 1 CURR TRIGGER
FLEXLOGIC OPERANDS
PMU 1 FREQ TRIGGER
PMU 1 VOLT TRIGGER
PMU 1 POWER TRIGGER
PMU 1 ROCOF TRIGGER
SETTING
PMU 1 USER TRIGGER:
Off = 0
OR
FLEXLOGIC OPERAND
PMU 1 TRIGGERED
to STAT bits of
the data frame
IA
I > PICKUP
I > PICKUP
I > PICKUP
OR
IB
IC
847010A1.CDR
SETTINGS
PKP
t
0
PMU 1 CURR TRIGGER PKP TIME:
0
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...