B-36
F60 Feeder Protection System
GE Multilin
B.4 MEMORY MAPPING
APPENDIX B
B
46B6
Incipient Cable Fault Detector 1 Pickup
0.1 to 10
pu
0.01
F001
50
46B7
Incipient Cable Fault Detector 1 Mode
0 to 1
---
1
F254
0 (Number of
Counts)
46B8
Incipient Cable Fault Detector 1 Trip Counts
1 to 10
---
1
F001
2
46B9
Incipient Cable Fault Detector 1 Time Window
0 to 1000
s
0.01
F003
1000
46BB
Incipient Cable Fault Detector 1 Reset Delay
0 to 65.535
s
0.001
F001
100
46BC
Incipient Cable Fault Detector 1 Target
0 to 2
---
1
F109
0 (Self-reset)
46BD
Incipient Cable Fault Detector 1 Events
0 to 1
---
1
F102
0 (Disabled)
46BE
...Repeated for Incipient Cable Fault Detector 2
Breaker Control (Read/Write Settings) (4 modules)
47D0
Breaker 1 Function
0 to 1
---
1
F102
0 (Disabled)
47D1
Breaker 1 Name
---
---
---
F206
“Bkr 1"
47D4
Breaker 1 Mode
0 to 1
---
1
F157
0 (3-Pole)
47D5
Breaker 1 Open
0 to 4294967295
---
1
F300
0
47D7
Breaker 1 Close
0 to 4294967295
---
1
F300
0
47D9
Breaker 1 Phase A / Three-pole Closed
0 to 4294967295
---
1
F300
0
47DB
Breaker 1 Phase B Closed
0 to 4294967295
---
1
F300
0
47DD
Breaker 1 Phase C Closed
0 to 4294967295
---
1
F300
0
47DF
Breaker 1 External Alarm
0 to 4294967295
---
1
F300
0
47E1
Breaker 1 Alarm Delay
0 to 65.535
s
0.001
F003
0
47E3
Breaker 1 Pushbutton Control
0 to 1
---
1
F102
0 (Disabled)
47E4
Breaker 1 Manual Close Recall Time
0 to 4294967295
s
0.001
F003
0
47E6
Breaker 1 Out of Service
0 to 4294967295
---
1
F300
0
47E8
Breaker 1 Block Open
0 to 4294967295
---
1
F300
0
47EA
Breaker 1 Block Close
0 to 4294967295
---
1
F300
0
47EC
Breaker 1 Phase A / Three-pole Opened
0 to 4294967295
---
1
F300
0
47EE
Breaker 1 Phase B Opened
0 to 4294967295
---
1
F300
0
47F0
Breaker 1 Phase C Opened
0 to 4294967295
---
1
F300
0
47F2
Breaker 1 Operate Time
0 to 65.535
s
0.001
F001
70
47F3
Breaker 1 Events
0 to 1
---
1
F102
0 (Disabled)
47F4
Reserved
0 to 65535
s
1
F001
0
47F5
...Repeated for Breaker 2
Demand (Read/Write Setting)
490A
Demand Current Method
0 to 2
---
1
F139
0 (Thermal
Exponential)
490B
Demand Power Method
0 to 2
---
1
F139
0 (Thermal
Exponential)
490C
Demand Interval
0 to 5
---
1
F132
2 (15 MIN)
490D
Demand Input
0 to 4294967295
---
1
F300
0
Demand (Read/Write Command)
490F
Demand Clear Record
0 to 1
---
1
F126
0 (No)
FlexCurves A and B (Read/Write Settings)
4910
FlexCurve A (120 items)
0 to 65535
ms
1
F011
0
4988
FlexCurve B (120 items)
0 to 65535
ms
1
F011
0
Modbus User Map (Read/Write Setting)
4A00
Modbus Address Settings for User Map (256 items)
0 to 65535
---
1
F001
0
User Displays Settings (Read/Write Setting) (16 modules)
4C00
User-Definable Display 1 Top Line Text
---
---
---
F202
“ “
4C0A
User-Definable Display 1 Bottom Line Text
---
---
---
F202
“ “
4C14
Modbus Addresses of Display 1 Items (5 items)
0 to 65535
---
1
F001
0
4C19
Reserved (7 items)
---
---
---
F001
0
4C20
...Repeated for User-Definable Display 2
4C40
...Repeated for User-Definable Display 3
4C60
...Repeated for User-Definable Display 4
4C80
...Repeated for User-Definable Display 5
Table B–10: MODBUS MEMORY MAP (Sheet 28 of 70)
ADDR
REGISTER NAME
RANGE
UNITS
STEP
FORMAT
DEFAULT
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...