5-162
F60 Feeder Protection System
GE Multilin
5.5 FLEXLOGIC
5 SETTINGS
5
5.5.7 FLEXELEMENTS
PATH: SETTING
FLEXLOGIC
FLEXELEMENTS
FLEXELEMENT 1(8)
A FlexElement is a universal comparator that can be used to monitor any analog actual value calculated by the relay or a
net difference of any two analog actual values of the same type. The effective operating signal could be treated as a signed
number or its absolute value could be used as per user's choice.
FlexElements run every half power cycle (every four protection passes).
The element can be programmed to respond either to a signal level or to a rate-of-change (delta) over a pre-defined period
of time. The output operand is asserted when the operating signal is higher than a threshold or lower than a threshold as
per user's choice.
FLEXELEMENT 1
FLEXELEMENT 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
FLEXELEMENT 1 NAME:
FxE1
Range: up to 6 alphanumeric characters
MESSAGE
FLEXELEMENT 1 +IN:
Off
Range: Off, any analog actual value parameter
MESSAGE
FLEXELEMENT 1 -IN:
Off
Range: Off, any analog actual value parameter
MESSAGE
FLEXELEMENT 1 INPUT
MODE: Signed
Range: Signed, Absolute
MESSAGE
FLEXELEMENT 1 COMP
MODE: Level
Range: Level, Delta
MESSAGE
FLEXELEMENT 1
DIRECTION: Over
Range: Over, Under
MESSAGE
FLEXELEMENT 1
PICKUP: 1.000 pu
Range: –90.000 to 90.000 pu in steps of 0.001
MESSAGE
FLEXELEMENT 1
HYSTERESIS: 3.0%
Range: 0.1 to 50.0% in steps of 0.1
MESSAGE
FLEXELEMENT 1 dt
UNIT: milliseconds
Range: milliseconds, seconds, minutes
MESSAGE
FLEXELEMENT 1 dt:
20
Range: 20 to 86400 in steps of 1
MESSAGE
FLEXELEMENT 1 PKP
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
FLEXELEMENT 1 RST
DELAY: 0.000 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
FLEXELEMENT 1 BLK:
Off
Range: FlexLogic operand
MESSAGE
FLEXELEMENT 1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
FLEXELEMENT 1
EVENTS: Disabled
Range: Disabled, Enabled
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...