![GE Grid Solutions F60 Instruction Manual Download Page 263](http://html.mh-extra.com/html/ge-grid-solutions/f60/f60_instruction-manual_571876263.webp)
GE Multilin
F60 Feeder Protection System
5-125
5 SETTINGS
5.4 SYSTEM SETUP
5
EXAMPLE: THE CREATION OF DIFFERENT DATA SETS
The aggregators allow the aggregation of phasors from multiple PMUs (with the same reporting rate) into a single custom
data set to optimize bandwidth when streaming.
Figure 5–45: EXAMPLE OF AGGREGATOR DATA SETS
CONFIGURATION EXAMPLE: CFG-2 BASED CONFIGURATION (USING IEC 61850-90-5)
The F60 is expected to send the CFG-2 file (IEEE C37.118 config. file) upon request from the upstream synchrophasor
devices (for example, P30) without stopping R-SV multicasting, as shown in the figure below. The primary domain control-
ler (PDC) does not need to use a stop/start data stream command if the UR protocol is set to IEC 61850-90-5 prior to
requesting the configuration via CFG-2 (IEEE C37.118 config. file). The CFG-2 request from the P30 can be on TCP/IP or
UDP/IP, however, R-SV data streaming is only UDP multicasts (not TCP).
Figure 5–46: CFG-2 BASED CONFIGURATION SOLUTION
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...