5.10 TESTING
5 SETTINGS
5
5.10.4 PHASOR MEASUREMENT UNIT TEST VALUES
PATH: SETTINGS
TESTING
PMU TEST VALUES
PMU 1 TEST VALUES
The relay must be in test mode to use the PMU test mode. That is, the
TESTING
TEST MODE FUNCTION
setting must be
“Enabled” and the
TESTING
TEST MODE INITIATE
initiating signal must be “On”.
PMU 1
TEST VALUES
PMU 1 TEST
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
PMU 1 VA TEST
MAGNITUDE: 500.00 kV
Range: 0.00 to 700.00 kV in steps of 0.01
MESSAGE
PMU 1 VA TEST
ANGLE: 0.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 VB TEST
MAGNITUDE: 500.00 kV
Range: 0.00 to 700.00 kV in steps of 0.01
MESSAGE
PMU 1 VB TEST
ANGLE: –120.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 VC TEST
MAGNITUDE: 500.00 kV
Range: 0.00 to 700.00 kV in steps of 0.01
MESSAGE
PMU 1 VC TEST
ANGLE: 120.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 VX TEST
MAGNITUDE: 500.00 kV
Range: 0.00 to 700.00 kV in steps of 0.01
MESSAGE
PMU 1 VX TEST
ANGLE: 0.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 IA TEST
MAGNITUDE: 1.000 kA
Range: 0.000 to 9.999 kA in steps of 0.001
MESSAGE
PMU 1 IA TEST
ANGLE: –10.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 IB TEST
MAGNITUDE: 1.000 kA
Range: 0.000 to 9.999 kA in steps of 0.001
MESSAGE
PMU 1 IB TEST
ANGLE: –130.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 IC TEST
MAGNITUDE: 1.000 kA
Range: 0.000 to 9.999 kA in steps of 0.001
MESSAGE
PMU 1 IC TEST
ANGLE: 110.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 IG TEST
MAGNITUDE: 0.000 kA
Range: 0.000 to 9.999 kA in steps of 0.001
MESSAGE
PMU 1 IG TEST
ANGLE: 0.00°
Range: –180.00 to 180.00° in steps of 0.05
MESSAGE
PMU 1 TEST
FREQUENCY: 60.000 Hz
Range: 20.000 to 60.000 Hz in steps of 0.001
MESSAGE
PMU 1 TEST
df/dt: 0.000 Hz/s
Range: –10.000 to 10.000 Hz/s in steps of 0.001
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...