5-74
F60 Feeder Protection System
GE Multilin
5.2 PRODUCT SETUP
5 SETTINGS
5
The fourth current input in a bank is called IG, and the fourth voltage input in a bank is called VX. For example, F2-IB desig-
nates the IB signal on terminal 2 of the CT/VT module in slot F.
If there are no CT/VT modules and analog input modules, no analog traces will appear in the file; only the digital traces will
appear.
The source harmonic indices appear as oscillography analog channels numbered from 0 to 23. These correspond
directly to the to the 2nd to 25th harmonics in the relay as follows:
Analog channel 0
↔
2nd harmonic
Analog channel 1
↔
3rd harmonic
...
Analog channel 23
↔
25th harmonic
5.2.9 DATA LOGGER
PATH: SETTINGS
PRODUCT SETUP
DATA LOGGER
The data logger samples and records up to 16 analog parameters at a user-defined sampling rate. This recorded data may
be downloaded to EnerVista UR Setup and displayed with
parameters
on the vertical axis and
time
on the horizontal axis.
All data is stored in non-volatile memory, meaning that the information is retained when power to the relay is lost.
For a fixed sampling rate, the data logger can be configured with a few channels over a long period or a larger number of
channels for a shorter period. The relay automatically partitions the available memory between the channels in use. Exam-
ple storage capacities for a system frequency of 60 Hz are shown in the following table.
DATA LOGGER
DATA LOGGER MODE:
Continuous
Range: Continuous, Trigger
MESSAGE
DATA LOGGER TRIGGER:
Off
Range: FlexLogic operand
MESSAGE
DATA LOGGER RATE:
60000 ms
Range: 15 to 3600000 ms in steps of 1
MESSAGE
DATA LOGGER CHNL
1:
Off
Range: Off, any FlexAnalog parameter. See Appendix A:
FlexAnalog Parameters for complete list.
MESSAGE
DATA LOGGER CHNL
2:
Off
Range: Off, any FlexAnalog parameter. See Appendix A:
FlexAnalog Parameters for complete list.
MESSAGE
DATA LOGGER CHNL
3:
Off
Range: Off, any FlexAnalog parameter. See Appendix A:
FlexAnalog Parameters for complete list.
↓
MESSAGE
DATA LOGGER CHNL 16:
Off
Range: Off, any FlexAnalog parameter. See Appendix A:
FlexAnalog Parameters for complete list.
MESSAGE
DATA LOGGER CONFIG:
0 CHNL x
0.0 DAYS
Range: Not applicable - shows computed data only
NOTE
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...