6-20
F60 Feeder Protection System
GE Multilin
6.3 METERING
6 ACTUAL VALUES
6
The metered values for real, reactive, and apparent power, as well as power factor, are displayed in this menu. The "SRC
1" text is replaced by whatever name was programmed by the user for the associated source (see
SETTINGS
SYSTEM
SETUP
SIGNAL SOURCES
).
When VTs are configured in wye, the F60 calculates power in each phase and three-phase power is measured as
S = V
A
x Î
A
+ V
B
x Î
B
+ V
C
x Î
C
(EQ 6.1)
When VTs are configured in delta, the F60 does not calculate power in each phase and three-phase power is measured as
S = V
AB
x Î
A
+ V
CB
x Î
C
(EQ 6.2)
where
S is the apparent power
V
A
, V
B
, V
C
, I
A
, I
B
, I
C
are phase voltage and phase current phasors
V
AB
and V
CB
are phase-to-phase voltage phasors
Î is the conjugate of I
g) ENERGY METERING
PATH: ACTUAL VALUES
METERING
SOURCE SRC 1
ENERGY
The metered values for real and reactive energy are displayed in this menu. The "SRC 1" text will be replaced by whatever
name was programmed by the user for the associated source (see
SETTINGS
SYSTEM SETUP
SIGNAL SOURCES
).
Because energy values are accumulated, these values should be recorded and then reset immediately prior to changing
CT or VT characteristics.
MESSAGE
SRC 1 APPARENT PWR
φ
a: 0.000 VA
MESSAGE
SRC 1 APPARENT PWR
φ
b: 0.000 VA
MESSAGE
SRC 1 APPARENT PWR
φ
c: 0.000 VA
MESSAGE
SRC 1 POWER FACTOR
3
φ
: 1.000
MESSAGE
SRC 1 POWER FACTOR
φ
a: 1.000
MESSAGE
SRC 1 POWER FACTOR
φ
b: 1.000
MESSAGE
SRC 1 POWER FACTOR
φ
c: 1.000
ENERGY
SRC 1
SRC 1 POS WATTHOUR:
0.000 Wh
MESSAGE
SRC 1 NEG WATTHOUR:
0.000 Wh
MESSAGE
SRC 1 POS VARHOUR:
0.000 varh
MESSAGE
SRC 1 NEG VARHOUR:
0.000 varh
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...