5-25
5 SETTINGS
5.2 PRODUCT SETUP
5
components. The cut-off operation applies to quantities used for metering, protection, and control, as well as those
used by communications protocols. Raw samples of the voltages available via oscillography are not subject cut-off.
The
CURRENT CUT-OFF LEVEL
and the
VOLTAGE CUT-OFF LEVEL
are used to determine the metered power cut-off levels. The
power cut-off level is calculated as shown below. For Delta connections:
(EQ 5.3)
For Wye connections:
(EQ 5.4)
(EQ 5.5)
where VT primary = VT secondary
×
VT ratio and CT primary = CT secondary
×
CT ratio.
For example, given the following settings:
CURRENT CUT-OFF LEVEL
: “0.02 pu”
VOLTAGE CUT-OFF LEVEL
: “1.0 V”
PHASE CT PRIMARY
: “100 A”
PHASE VT SECONDARY
: “66.4 V”
PHASE VT RATIO
: “208.00 : 1"
PHASE VT CONNECTION
: “Delta”.
We have:
CT primary = “100 A”, and
VT primary =
PHASE VT SECONDARY
x
PHASE VT RATIO
= 66.4 V x 208 = 13811.2 V
The power cut-off is therefore:
power cut-off = (
CURRENT CUT-OFF LEVEL
×
VOLTAGE CUT-OFF LEVEL
×
CT primary
×
VT primary)/VT secondary
= (
×
0.02 pu
×
1.0 V
×
100 A
×
13811.2 V) / 66.4 V
= 720.5 watts
Any calculated power value below this cut-off will not be displayed. As well, the three-phase energy data will not accumu-
late if the total power from all three phases does not exceed the power cut-off.
Lower the VOLTAGE CUT-OFF LEVEL and CURRENT CUT-OFF LEVEL with care as the relay accepts lower sig-
nals as valid measurements. Unless dictated otherwise by a specific application, the default settings of “0.02 pu” for
CURRENT CUT-OFF LEVEL and “1.0 V” for VOLTAGE CUT-OFF LEVEL are recommended.
5.2.3 CLEAR RELAY RECORDS
PATH: SETTINGS
PRODUCT SETUP
CLEAR RELAY RECORDS
CLEAR RELAY
RECORDS
CLEAR FAULT REPORTS:
Off
Range: FlexLogic operand
MESSAGE
CLEAR EVENT RECORDS:
Off
Range: FlexLogic operand
MESSAGE
CLEAR OSCILLOGRAPHY?
No
Range: FlexLogic operand
MESSAGE
CLEAR DATA LOGGER:
Off
Range: FlexLogic operand
MESSAGE
CLEAR ARC AMPS 1:
Off
Range: FlexLogic operand
MESSAGE
CLEAR ARC AMPS 2:
Off
Range: FlexLogic operand
3-phase power cut-off
3
CURRENT CUT-OFF LEVEL
×
VOLTAGE CUT-OFF LEVEL
VT primary
×
CT primary
×
×
VT secondary
------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
=
3-phase power cut-off
3
CURRENT CUT-OFF LEVEL
×
VOLTAGE CUT-OFF LEVEL
VT primary
×
CT primary
×
×
VT secondary
--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
=
per-phase power cut-off
CURRENT CUT-OFF LEVEL
VOLTAGE CUT-OFF LEVEL
VT primary
×
CT primary
×
×
VT secondary
----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
=
3
NOTE
Summary of Contents for F60
Page 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Page 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Page 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Page 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Page 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Page 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Page 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Page 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Page 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Page 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Page 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Page 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...