5-294
F60 Feeder Protection System
GE Multilin
5.8 INPUTS/OUTPUTS
5 SETTINGS
5
c) REMOTE DEVICES: ID OF DEVICE FOR RECEIVING GSSE/GOOSE MESSAGES
PATH: SETTINGS
INPUTS/OUTPUTS
REMOTE DEVICES
REMOTE DEVICE 1(16)
Remote devices are available for setting purposes. A receiving relay must be programmed to capture messages from only
those originating remote devices of interest. This setting is used to select specific remote devices by entering (bottom row)
the exact identification (ID) assigned to those devices.
The
REMOTE DEVICE 1 ETYPE APPID
setting is only used with GOOSE messages; they are not applicable to GSSE mes-
sages. This setting identifies the Ethernet application identification in the GOOSE message. It should match the corre-
sponding settings on the sending device.
The
REMOTE DEVICE 1 DATASET
setting provides for the choice of the F60 fixed (DNA/UserSt) dataset (that is, containing
DNA and UserSt bit pairs), or one of the configurable datasets.
Note that the dataset for the received data items must be made up of existing items in an existing logical node. For this rea-
son, logical node GGIO3 is instantiated to hold the incoming data items. GGIO3 is not necessary to make use of the
received data. The remote input data item mapping takes care of the mapping of the inputs to remote input FlexLogic oper-
ands. However, GGIO3 data can be read by IEC 61850 clients.
5.8.6 REMOTE INPUTS
PATH: SETTINGS
INPUTS/OUTPUTS
REMOTE INPUTS
REMOTE INPUT 1(32)
Remote Inputs that create FlexLogic operands at the receiving relay are extracted from GSSE/GOOSE messages originat-
ing in remote devices. Each remote input can be selected from a list consisting of: DNA-1 through DNA-32, UserSt-1
through UserSt-32, and Dataset Item 1 through Dataset Item 32. The function of DNA inputs is defined in the IEC 61850
specification and is presented in the IEC 61850 DNA Assignments table in the
Remote Outputs
section. The function of
UserSt inputs is defined by the user selection of the FlexLogic operand whose state is represented in the GSSE/GOOSE
message. A user must program a DNA point from the appropriate FlexLogic operand.
Remote input 1 must be programmed to replicate the logic state of a specific signal from a specific remote device for local
use. This programming is performed via the three settings shown above.
The
REMOTE INPUT 1 ID
setting allows the user to assign descriptive text to the remote input. The
REMOTE IN 1 DEVICE
setting
selects the remote device which originates the required signal, as previously assigned to the remote device via the setting
REMOTE DEVICE (16) ID
(see the
Remote Devices
section). The
REMOTE IN 1 ITEM
setting selects the specific bits of the
GSSE/GOOSE message required.
The
REMOTE IN 1 DEFAULT STATE
setting selects the logic state for this point if the local relay has just completed startup or
the remote device sending the point is declared to be non-communicating. The following choices are available:
REMOTE DEVICE 1
REMOTE DEVICE 1 ID:
Remote Device 1
Range: up to 20 alphanumeric characters
MESSAGE
REMOTE DEVICE 1
ETYPE APPID: 0
Range: 0 to 16383 in steps of 1
MESSAGE
REMOTE DEVICE 1
DATASET: Fixed
Range: Fixed, GOOSE 1 through GOOSE 16
REMOTE INPUT 1
REMOTE INPUT 1 ID:
Remote Ip 1
Range: up to 12 alphanumeric characters
MESSAGE
REMOTE IN 1 DEVICE:
Remote Device 1
Range: Remote Device 1 to Remote device 16
MESSAGE
REMOTE IN 1 ITEM:
None
Range: None, DNA-1 to DNA-32, UserSt-1 to UserSt-32,
Config Item 1 to Config Item 32
MESSAGE
REMOTE IN 1 DEFAULT
STATE: Off
Range: On, Off, Latest/On, Latest/Off
MESSAGE
REMOTE IN 1
EVENTS: Disabled
Range: Disabled, Enabled
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...