GE Multilin
F60 Feeder Protection System
5-217
5 SETTINGS
5.6 GROUPED ELEMENTS
5
5.6.10 VOLTAGE ELEMENTS
a) MAIN MENU
PATH: SETTINGS
GROUPED ELEMENTS
SETTING GROUP 1(6)
VOLTAGE ELEMENTS
These protection elements can be used for a variety of applications such as:
•
Undervoltage Protection:
For voltage sensitive loads, such as induction motors, a drop in voltage increases the
drawn current which may cause dangerous overheating in the motor. The undervoltage protection feature can be used
to either cause a trip or generate an alarm when the voltage drops below a specified voltage setting for a specified time
delay.
•
Permissive Functions:
The undervoltage feature may be used to block the functioning of external devices by operat-
ing an output relay when the voltage falls below the specified voltage setting. The undervoltage feature may also be
used to block the functioning of other elements through the block feature of those elements.
•
Source Transfer Schemes:
In the event of an undervoltage, a transfer signal may be generated to transfer a load
from its normal source to a standby or emergency power source.
VOLTAGE ELEMENTS
PHASE
UNDERVOLTAGE1
MESSAGE
PHASE
UNDERVOLTAGE2
MESSAGE
PHASE
UNDERVOLTAGE3
MESSAGE
PHASE
OVERVOLTAGE1
MESSAGE
PHASE
OVERVOLTAGE2
MESSAGE
PHASE
OVERVOLTAGE3
MESSAGE
NEUTRAL OV1
MESSAGE
NEUTRAL OV2
MESSAGE
NEUTRAL OV3
MESSAGE
NEG SEQ OV1
MESSAGE
NEG SEQ OV2
MESSAGE
NEG SEQ OV3
MESSAGE
AUXILIARY UV1
MESSAGE
AUXILIARY UV2
MESSAGE
AUXILIARY OV1
MESSAGE
AUXILIARY OV2
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...