GE Multilin
F60 Feeder Protection System
5-111
5 SETTINGS
5.4 SYSTEM SETUP
5
5.4.5 DISCONNECT SWITCHES
PATH: SETTINGS
SYSTEM SETUP
SWITCHES
SWITCH 1(16)
The disconnect switch control element contains the auxiliary logic for status and serves as the interface for opening and
closing of disconnect switches from SCADA or through the front panel interface. The disconnect switch control element can
be used to create interlocking functionality. For greater security in determination of the switch pole position, both the 89/a
and 89/b auxiliary contacts are used with reporting of the discrepancy between them. The number of available disconnect
switches is four per breaker.
To use this element, configure the contact outputs that open and close the disconnect switch to use FlexLogic operands
SWITCH 1 OFF CMD
and
SWITCH 1 ON CMD
, and configure the disconnect switch control element's inputs as outlined here.
•
SWITCH 1 FUNCTION:
This setting enables and disables the operation of the disconnect switch element.
•
SWITCH 1 NAME:
Assign a user-defined name (up to six characters) to the disconnect switch. This name will be used
in flash messages related to disconnect switch 1.
SWITCH 1
SWITCH 1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
SWITCH 1 NAME:
SW 1
Range: up to 6 alphanumeric characters
MESSAGE
SWITCH 1 MODE:
3-Pole
Range: 3-Pole, 1-Pole
MESSAGE
SWITCH 1 OPEN:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1 BLK OPEN:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1 CLOSE:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1 BLK CLOSE:
Off
Range: FlexLogic operand
MESSAGE
SWTCH 1
Φ
A/3P CLSD:
Off
Range: FlexLogic operand
MESSAGE
SWTCH 1
Φ
A/3P OPND:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1
Φ
B CLOSED:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1
Φ
B OPENED:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1
Φ
C CLOSED:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1
Φ
C OPENED:
Off
Range: FlexLogic operand
MESSAGE
SWITCH 1 TOPERATE:
0.070 s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
SWITCH 1 ALARM
DELAY: 0.000
s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
SWITCH 1 EVENTS:
Disabled
Range: Disabled, Enabled
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...