F60 Feeder Protection System
GE Multilin
5.2 PRODUCT SETUP
5 SETTINGS
5
Figure 5–23: DUAL-CHANNEL CLOSED LOOP (DUAL-RING) CONFIGURATION
In the above application, the following settings should be applied. For UR-series IED 1:
DIRECT OUTPUT DEVICE ID:
“1”
DIRECT I/O CH1 RING CONFIGURATION:
“Yes”
DIRECT I/O CH2 RING CONFIGURATION:
“Yes”
For UR-series IED 2:
DIRECT OUTPUT DEVICE ID:
“2”
DIRECT I/O CH1 RING CONFIGURATION:
“Yes”
DIRECT I/O CH2 RING CONFIGURATION:
“Yes”
For UR-series IED 3:
DIRECT OUTPUT DEVICE ID:
“3”
DIRECT I/O CH1 RING CONFIGURATION:
“Yes”
DIRECT I/O CH2 RING CONFIGURATION:
“Yes”
In this configuration the following delivery times are expected (at 128 kbps) if both the rings are healthy:
IED 1 to IED 2: 0.2 of power system cycle;
IED 1 to IED 3: 0.2 of power system cycle;
IED 2 to IED 3: 0.2 of power system cycle.
The two communications configurations could be applied to both permissive and blocking schemes. Speed, reliability and
cost should be taken into account when selecting the required architecture.
b) CRC ALARM CH1(2)
PATH: SETTINGS
PRODUCT SETUP
DIRECT I/O
CRC ALARM CH1(2)
The F60 checks integrity of the incoming direct input and output messages using a 32-bit CRC. The CRC alarm function is
available for monitoring the communication medium noise by tracking the rate of messages failing the CRC check. The
monitoring function counts all incoming messages, including messages that failed the CRC check. A separate counter adds
up messages that failed the CRC check. When the failed CRC counter reaches the user-defined level specified by the
CRC
ALARM CH1 THRESHOLD
setting within the user-defined message count
CRC ALARM 1 CH1 COUNT
, the
DIR IO CH1 CRC ALARM
FlexLogic operand is set.
When the total message counter reaches the user-defined maximum specified by the
CRC ALARM CH1 MESSAGE COUNT
set-
ting, both the counters reset and the monitoring process is restarted.
CRC ALARM CH1
CRC ALARM CH1
FUNCTION: Disabled
Range: Enabled, Disabled
MESSAGE
CRC ALARM CH1
MESSAGE COUNT: 600
Range: 100 to 10000 in steps of 1
MESSAGE
CRC ALARM CH1
THRESHOLD: 10
Range: 1 to 1000 in steps of 1
MESSAGE
CRC ALARM CH1
EVENTS: Disabled
Range: Enabled, Disabled
842715A1.CDR
UR IED 1
TX1
RX2
TX2
RX1
UR IED 2
RX2
TX1
RX1
TX2
UR IED 3
RX1
TX2
TX1
RX2
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...